Previous in Forum: Need Some Help in Designing Plate Bending Machine.   Next in Forum: Rope Guide for Winches
Close
Close
Close
3 comments
Rate Comments: Nested
Participant

Join Date: Dec 2010
Posts: 1

Troubleshooting a CB Firetube Boiler

12/31/2010 9:46 AM

Working on a 2001 cleaver brooks CEW200-300 fire tube boiler, I am continuously running into the problem of having it shut off in interlock. I have replaced atomizing air switch and oil pump, to no avail. Any suggestions to check or what may be the issue would be greatly appreciated.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#1

Re: Troubleshooting a CB Firetube Boiler

12/31/2010 10:41 PM

I have had the modulating dampers get out of sync in the past which has caused interlock failure. The best bet is to replace the damper motor once they get out of sync you can adjust it but they will slip again.

Or the linkage is binding on the prepurge causing the interlock drop outs.

__________________
To be or not to be........ok that's a trick question.
Register to Reply
Commentator
Safety - Hazmat - R&D Engineer/Inventor

Join Date: Apr 2009
Location: South Florida
Posts: 88
Good Answers: 8
#2

Re: Troubleshooting a CB Firetube Boiler

01/01/2011 10:18 AM

What model is the flame safe guard system? ie; CB 780 , does it have an expanded annunciator CB783?

At what stage does it lockout? Does it lockout during the start up or while running normally? Does it get past the purge cycle? Have you check the Pre-ignition interlocks (fuel valve proof of closure) and flame signal check during Standby and Pre-Purge. If running have you checked flame scanner; aimed at flame correct, dirty lens, amp signal is adequate (measured with meter)? Is it giving a lockout code (if annunciated) .

As you can see more information is needed to determine the cause, simply replacing all of the components without finding the cause can be a waste of time and money.

I once worked on a new boiler at a hospital that would only lockout when the makeup air temperature in the boiler room dropped to low. The endless search to find the cause, believe it or not was the cold air. The makeup air heater was steam heated and once steam was lost it could not heat the air coming into the boiler room. The fuel/air mixture (O2 density changed) would change and the scanner could not see the flame and the boiler would lock out. We ended up using a magnification lens on a more expensive IR scanner. All systems check out repeatedly during the trouble shooting, replacing parts was futile.

I would suggest calling in the CB FSR.

__________________
masterblaster
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2010
Location: St Louis MO USA
Posts: 224
Good Answers: 7
#3

Re: Troubleshooting a CB Firetube Boiler

01/01/2011 2:49 PM

Dear DMR, Try this ..........http://www.boilersupplies.com/warrick/ Your warrick lwco control is now been discontinued. Replace it and buy a spare too, then come back and give a GA to the right answer.

__________________
klearzen
Register to Reply
Register to Reply 3 comments