Main Breaker Based on 3Ph or 1Ph

01/03/2011 12:35 AM

As we know that 1Ph draw more current and 3Ph draw less current to balance the VA rating.I have some confusion during load calculation. In 3 phase panel load center, some load as a single phase(2P breaker,Ph&N) and some load as a 3Ph(R,Y,B),so our final load calculation based on 3ph(square root 3) or 1Ph for main breaker,. So could any one tell me the answer

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#1

Re: Main breaker based on 3Ph or 1Ph

01/03/2011 1:04 AM

Connect a power analyser and record Amp drwan in each phase during working hours and decide the rating of CB.If load is unbalanced you should balance it.

__________________
pnaban
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Main breaker based on 3Ph or 1Ph

01/03/2011 4:09 AM

The breaker must be sized so as to prevent the cables taking too much current. British Standard 7671 tells all.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#3
In reply to #2

Re: Main breaker based on 3Ph or 1Ph

01/03/2011 2:25 PM

PWSlack is correct, but I'd amplify his answer a little (I did give him a GA):

  • The NEC also "tells all".
  • The outgoing breakers from this panel are sized to protect the conductors going to the loads. If you also want more precise protection (like for a motor), you need to use supplementary protection (like a motor starter with overload protection).
Reply
Reply to Forum Thread 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

pnaban (1); PWSlack (1); rhkramer (1)

Previous in Forum: Voltage Setting in GCP30 Series   Next in Forum: High Electric Bill for Residential House

Advertisement