Inron Loss and Full Load Copper Loss for Transformers

01/03/2011 2:13 AM

Dear All,

Wish you all a very happy and prosperous New Year 2011.

I have one query -

Could you kindly let me know the rated Core Loss and Full Load Copper Loss for the following rating of transformers -

1. 7500 KVA,

2. 3000 KVA,

3. 2000 KVA,

4. 1500 KVA

Your suggestions will be highly appreciated

Regards,

Rooney

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Inron Loss and Full Load Copper Loss for Transformers

01/03/2011 4:05 AM

The best thing to do is ring the manufacturer when his offices re-open after the New Year holidays.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#2

Re: Inron Loss and Full Load Copper Loss for Transformers

01/03/2011 6:56 AM

My ancient textbook gives examples of (50Hz) :-

  1. 1000 kVA 3 phase 6.6/0.44 kV Copper loss 6.6 kW a 75 Celsius copper temperature, Iron loss 3.7 kW Full LOad. Hence Efficiency ~99%.
  2. 15000 kVA, 3 phase 33/6.6 kV Copper loss 99 kW a 75 Celsius copper temperature, Iron loss 26 kW Full Load. Hence Efficiency ~99.2%.

But single phase will be worse and low voltage/high current worse efficiency. In practice, copper temperature will depend on ambient and previous loading. Application where load % is typically low will emphasize low core loss over low copper loss because core loss is 24 hour/day cost for supplier.

Register to Reply
Anonymous Poster
#3

Re: Inron Loss and Full Load Copper Loss for Transformers

01/04/2011 1:15 AM

THIS IS AVAILABLE IN THE MANUFACTURERS DATASHEET.

HOWEVER IF YOU WANT TO KNOW THE TREND FOR THE BEST MANUFACTURERS THE NO LOAD LOSSES SHALL BE LESS THAN 1%,AND THE TOTAL LOSSES ARE A TRADE OF BETWEEN THE PRICES BETWEEN THE GOOD AND BAD MANUFACTURER.THE END USER HAS TO COMPARE THE COST REDUCTION VERSES LOSSES IN ENERGY FOR THE ENTIRE LIFESPAN OF THE TRANSFORMER .

Register to Reply
Anonymous Poster
#4

Re: Inron Loss and Full Load Copper Loss for Transformers

01/04/2011 1:53 AM

Please refer AC machines by MG SAY. It gives the complete procedure

Register to Reply
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#5

Re: Inron Loss and Full Load Copper Loss for Transformers

01/04/2011 10:50 AM

There is no such thing as RATED, . . or STANDARD loss for power transformers.

Each manufacturer will provide numbers on losses for his transformers, . . . and even these will vary according to application.

Losses will also depend on the transformer cooling - "dry type" or "liquid immersed" . .

HOWEVER, the US DOE Rule suggests efficiencies:

1,500 kVA - 99.14% - dry type, 99.42% - oil immersed.

2,500 kVA - 99.31% - dry type, 99.49% - oil immersed.

No numbers provided for transformers above 2,500 kVA.

Oleh

Register to Reply
Anonymous Poster
#6

Re: Inron Loss and Full Load Copper Loss for Transformers

01/04/2011 12:54 PM

Go to the Data Sheet of the items

Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

67model (1); Anonymous Poster (3); olehwi (1); PWSlack (1)

Previous in Forum: High Electric Bill for Residential House   Next in Forum: TRV Voltage for Circuit Breaker
You might be interested in: KVA Meters, Transformers, Electronic Transformers

Advertisement