Short Circuit Current 2

01/03/2011 9:21 AM

Happy new year everybody,

Very old question regaridng to SC current, What should the SC capacity of MCB be if I got the main MCCB rated at 10kA.

I have 03 options: 10kA, 5kA, and 14kA of 64A MCB. It is intent to install the one 5kA MCB for the additional line to provide power for several portable power tool and a container office.

Is there any problem if I choose 14kA 64A MCB?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Short Circuit Current 2

01/03/2011 10:55 AM

Happy new year to you too....

Well, you can use any breaker anywhere, provided that at least one of them has a higher capacity than what the system can deliver.

i know from your past postings that you are no newcomer to this....

It may be very informative for you to study discrimination, cascading, time based, energy based, current based ... there is a wealth of knowledge available out there. Specially ECT 167 from Schneider Electric...

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Short Circuit Current 2

01/03/2011 1:39 PM

So you mean that will be correct to have main breaker MCCB 10kA and MCB can be 14kA???.....

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: Short Circuit Current 2

01/03/2011 8:54 PM

Not normal. The upstream CB should have higher SC capacity.

But technically not wrong. Remember that MCBs are almost always current-limiting. Having lower inertia than a 3-pole MCCB, the MCB will act faster than the MCCB, and isolate the faulty feeder before the MCCB acts. Good discrimination achieved. Provided that the system fault level is <10kA at any point, no harm is using an MCB with a higher capacity isn't it? That's what the OP asked.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Anonymous Poster
#4
In reply to #3

Re: Short Circuit Current 2

01/04/2011 12:09 AM

well I understood. so we can drink 100ml water in cup or in a big barrel. Not normal, but technically not wrong. isnt it?..

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #4

Re: Short Circuit Current 2

01/04/2011 12:26 AM

Well, yes. However, a 14kA MCB is likely to clear a 10kA fault better than a 10kA MCB.

Just like the Ferrari here will do much better than the others around it once it reaches the DND flyway at Delhi...at the moment it is crawling @ 10kmph

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#7
In reply to #5

Re: Short Circuit Current 2

01/04/2011 2:46 AM

Kvsridhar:

The car looks very cool, is that your car?

Thank you for your comment, here I am considering of the coordination. Let's say 14kA MCB is better than 10kA MCB. But since I am having one main 10kA MCCB, so if I choose the branch 14kA MCB, is it good for coordination? If I choose the MCB a bit lower, is there any advantage?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#8
In reply to #7

Re: Short Circuit Current 2

01/04/2011 4:03 AM

That Ferrari ? Mine ? i have a 25:1 scale model. That is the closest i can get to one

As i said before, you need to study coordination systems, very interesting.

Let us say that you use a 14kA MCB downstream of the 10kA MCCB. A short-circuit happens in one of the feeders. Remember that it can't be >10kA, preferably much less (You would be prudent to use a 10kA CB if your system is not more than 7.5kA, otherwise your system is at risk).Now let us say the fault is 5kA. The 14kA MCB will clear it easily, and the MCCB should not trip. So you don't lose power to the healthy feeders. This is good coordination.

An MCB with lower capacity will be perhaps cheaper, no technical advantage. Nevertheless, you are not getting any great advantage using a 14kA MCB either.

What is the prospective SC level in your system anyway?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#9
In reply to #7

Re: Short Circuit Current 2

01/04/2011 5:00 AM

10kA, 5kA, 14kA these are the SC capacities the MCB or MCCB can handle without breaking down. These are not the tripping settings for the flowing currents. To select the correct one that will serve your purpose, you need to work out the SC current of the circuit downstream of the MCB (your question...). In any case, if the upstream MCCB is already rated 10KA, a 14kA will seem over-rated just because it will cost more only! It does not help selective tripping or affect the tripping setting of the MCB. Therefore, you select the appropriate MCB with the correct kA capacity that will exceed the maximum SC current on that branch of the circuit. Over sizing only hit your pocket. Undersizing can be desastrous in SC situation.

Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#12
In reply to #9

Re: Short Circuit Current 2

01/04/2011 9:04 AM

Ok, I will try to get straight to the point and we will have more serious sondieration. Let's not say about B,C or BC curves.

If your house has 02 floors and power is provided by one 60A-10kA MCB at the gate (presume the maximum SC current would be 10kA in this case). Then, you will install the same 10kA for MCBs, one for the first floor and one for the second floor.

Situation will occur like this. You have a SC at the very very end of your household power system at the 2nd floor and the MCB of the second floor trips. But thing would be Ok if you just need to check and the fault is allocated then you switch back the MCB. But, if the main MCB at the gate also tripped. This would annoy you by making a phone to the Power company (here we say power company) to switch back the power for you.

What does this situation say? If this is a bad coordination, then how we could improve it?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#13
In reply to #12

Re: Short Circuit Current 2

01/04/2011 10:20 AM

i repeat, you need to read up on discrimination, cascading etc.

Coming to this specific case of one residential building with two floors, you can expect "Partial discrimination" as opposed to full discrimination up to 10kA. Let me try to explain with this image...

Left curve - If the fault level is ≤IB, only the downstream MCB will trip, the other floor will not suffer a blackout. If the fault is higher, both will trip, entire building will have blackout.

Right curve - The threshold of the "partial discrimination" is much higher.

Anyway, when you have a short circuit at the end of a residential circuit, the impedances restrict the fault to low values. In my 3-floor, 6-flat building, the prospective fault at any flat's incoming is ≈ 2kA.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Anonymous Poster
#14
In reply to #13

Re: Short Circuit Current 2

01/04/2011 12:18 PM

Have they used oversized conductors???.....

Register to Reply Score 2 for Off Topic
Anonymous Poster
#15
In reply to #13

Re: Short Circuit Current 2

01/04/2011 12:20 PM

What is the kA rating of MCB used in your flat?? 14kA?

Register to Reply Score 2 for Off Topic
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#16
In reply to #13

Re: Short Circuit Current 2

01/05/2011 10:29 AM

Kvsridhar:

Thank you for your kind explanation. If you dont mind my questions, I will keep on asking that if the SC current ~2KA due to adding up the impedance. So, there would be no difference if I choose 5kA or 10kA or even 14kA MCB for each floor?

I mean it there is a fault and its SC current is at ~2kA, 5kA, 10kA, ot 14KA MCBs will work pretty fine on this. Ok, it is clear. But it will not affect to the upstream 60A MCB at the gate? We will not get blackout on the total area?

Additioanlly, if we have much stronger SC current let;s say 10KA, ( I dont know how if we can get this SC current while our system is rated at 2kA). It is sure that downstream MCB will trip but we will not sure that if the upstream MCB will trip or not? Is my though correct?

Thank you so much in advance,

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#17
In reply to #16

Re: Short Circuit Current 2

01/05/2011 11:00 AM

There will be some difference when you use MCBs of different capacities, not significant to the user though.

i mentioned "Partial discrimination"....this means that only the downstream CB will trip up to some low value of SC current, and above that, both may trip, may not trip. It may be that the upstream MCCB may try to open, but since the downstream MCB clears the fault, may re-close. All explained elegantly in the Schneider papers. Do you want the link?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#6

Re: Short Circuit Current 2

01/04/2011 2:43 AM

If it is resistive or semiconductor load go for 5kA; higher the inductive load go for higher KA.

__________________
Subramanyam
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#10

Re: Short Circuit Current 2

01/04/2011 6:45 AM

Happy new year to all.

Apart from selection of short circuit rating as already discussed, selection of charactiristic curve of MCB is very improtant depending of load. For example for lighting load B curve is correct; for motor load( airconditioner ) C curve is the choice etc.

__________________
Manindra
Register to Reply
Anonymous Poster
#11
In reply to #10

Re: Short Circuit Current 2

01/04/2011 7:58 AM

if you want to connect light and motor, use BC curve.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#18
In reply to #11

Re: Short Circuit Current 2

01/05/2011 1:37 PM

It would be most unusual for lighting and motors to be wired downstream of the same breaker.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856