problem with low frequency

01/04/2011 1:01 PM

I have a 11kw prime power generator 220v, 50hz, single phase, 1550 rpm, connected to ATS and VTMS ( Voltage and temperature monitoring system). The generator is showing low frequency alarm and shutting down itself while it is in automode with Microprocessor control panel DSE5220. But it runs manually. But we need to run it auto mode.

Please kindly advise us on the snag.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: problem with low frequency

01/04/2011 5:16 PM

Is it overloaded?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Jan 2011
Posts: 3
#2
In reply to #1

Re: problem with low frequency

01/05/2011 12:25 AM

Dear PWSlack,

No it is not overloaded !

Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#3

Re: problem with low frequency

01/05/2011 12:48 AM

Have you physically checked the actual rpm?

50 Hz should be 1500 rpm (loaded). So 1550 should be alarming 'high'.

Possibly your microprocessors frequency sensing is out, or its tachometer is out.

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Associate

Join Date: May 2010
Location: NC, USA
Posts: 34
Good Answers: 1
#4

Re: problem with low frequency

01/05/2011 6:52 AM

It sound as though the DSE5220 is set to run at 60hz even though the voltage regulator is set to 50hz. Make sure your settings in the DSE match the AVR. Then check your governer to make sure it's not overspeeding - I usually have to adjust the RPM a bit to get the tack "Just so".