HVAC

01/07/2011 12:44 PM

thank you guys for the advice you gave about cleaning shell tube for the plantroom ,its now working fine after the service.I commissioned 4x 54000btu ACs yesterday .The running pressure was 40 to 45 psi.ambient temperature was 22degrees set temperature was 18degrees and room temperature before AC was 20degrees .Is my refrigerant ,r22, ok,or i need to add more .My machines are working perfectly.Is my refrigerent level okey since during hot season we usually charge these machines upto 60psi.Will i not have the problem of low cooling during hot season,or ,is the low pressure being caused by generally low temperatures , .

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: HVAC

01/08/2011 4:11 AM

Do you by chance have an R-22 saturated pressure/temperature table or chart, so that you (and we) can see if your system readings make sense? The phrase "charge these machines up to 60 psi" doesn't compute too well.