Question About Air Volumes...

01/07/2011 3:34 PM

Afternoon all...

I am an electrical guy and as such, I am looking to verify a few core concepts.

Given a wet well for a sanitary sewer that has a volume of, for argument sakes, of say 12 cubic meters.

We equip the wet well with a supply fan and an exhaust fan. The purpose of the fans are to ensure ventilation of the wet well as per NFPA 820.

The supply fan is setup to supply 144 cubic meters of air per hour (to give us 12 changes of air per hour).

We must ensure that the area in the wet well is a minimum of -0.1 in water column with respect to ambient air.

We can achieve the required differential by driving the exhaust fan greater then the supply fan so that the whole volume of air in the wet well ends up negative with respect to ambient.

Is my logic sound?

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Question about Air Volumes...

01/07/2011 4:46 PM

I may be talking out the top of my head, but why have 2 fans? One exhaust fan and a slightly restricted inlet should give the required negative pressure in the chamber while allowing the required air flow.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2
In reply to #1

Re: Question about Air Volumes...

01/07/2011 5:20 PM

The two fans are required by the NFPA standard.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Question about Air Volumes...

01/07/2011 6:11 PM

What happens when one fan fails?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5
In reply to #3

Re: Question about Air Volumes...

01/07/2011 7:28 PM

They must be interlocked with the alarm system for the wet well system. In Canada, they must also be interlocked with all of the electrical equipment in the wet well.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: Question About Air Volumes...

01/07/2011 7:11 PM

OK have two exhaust fans. One in one out doesn't make sense. If the outlet fan fails you've got a pressurised chamber.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Jun 2010
Location: St Louis MO USA
Posts: 224
Good Answers: 7
#6

Re: Question About Air Volumes...

01/07/2011 7:28 PM

Dear North, I believe you can achieve what your driving towards with Two equal fans for a balanced draft ..... ADJUSTED.... to maintain a negative pressure. I do not have access to NFPA 820 /STANDARD FOR FIRE PROTECTION IN WASTEWATER TREATMENT AND COLLECTION FACILITIES. You will be able to locate numerous Blower companies on Globalspecs.

__________________
klearzen
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#7
In reply to #6

Re: Question About Air Volumes...

01/07/2011 7:33 PM

So whether you over drive the exhaust or restrict the supply, my premise is pretty much the same as what you mentioned. I can see where properly adjusted dampers on the inlet side could do what I need to see happen.

Thanks for the input.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Associate

Join Date: Jan 2009
Posts: 29
Good Answers: 1
#8
In reply to #7

Re: Question About Air Volumes...

01/07/2011 10:48 PM

Dampers should not be used in wet well ventialtion. Installing a VFD on your makeup air unit, or oversizeing your exhaust fan are your two best options.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#10
In reply to #7

Re: Question About Air Volumes...

01/08/2011 3:43 AM

Your fan capacity is decided by 12 times air changes per hour. Install two exhaust fans of same capacity. Only one should run, in case of failure, other fan should start automatically.

Slight vacuum of 0.1 in can be achieved easily by adjusting the openings for air inlet. Inlet lovers can be provided at appropriate places ensuring proper circulation of air before getting exhausted by the fan.

Register to Reply
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#12
In reply to #7

Re: Question About Air Volumes...

01/09/2011 9:17 AM

Along the same line as Klearzen.

You could use a single double shafted blower with one end, drawing or exhausting more than the other. This could be done by dampers.

With only one motor you may be able to included a second unit as back up, or a lead lag situation..

Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#9

Re: Question About Air Volumes...

01/07/2011 11:18 PM

What type of fan it is . Is it axial type or propeller type or blower. If it is blower is it forward or backward or normal curved ones. As the systems is designed as per the NFPA standards it is presumed required interlocking between the fans have been incorporated in the system design.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#11

Re: Question About Air Volumes...

01/08/2011 12:53 PM

My thanks to all who offered comment... enjoy your day.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Power-User

Join Date: May 2006
Posts: 142
Good Answers: 3
#13

Re: Question About Air Volumes...

01/09/2011 6:44 PM

YOU FANS CAN BE CONFIGURED TO TO MAINTAIN THE NEGATIVE WITH VFD'S CONTROLLED BY SIGNAL FROM DIFFERENTIAL PRESSURE TRANSMITTER WITH HIGH PRESSURE SIDE PIPED TO ATMOSPHERE AND LOW SIDE IN TANK A CHEAP CONFIGURABLE CONTROLLER CAN ALSO RECIEVE THE SIGNAL FROM THE DPT AND OUTPUT THE PROPER SIGNAL TO THE VFD'S AND SHUTDOWN THE FANS IF ONE DROPS AND THE CONDITION BECOMES A PROBLEM. iT COULD ALSO OUTPUT TO ANY FORMS OF ALARM YOU PREFER. vERY SIMILAR OPERATING SEQUENCE TO PHARMACY ROOMS, WE DO IT ALL THE TIME. PLEASE EXCUSE THE CAPS, I CAN'T TYPE AND I WON'T RETYPE.

Register to Reply
Power-User

Join Date: Feb 2010
Posts: 103
Good Answers: 2
#14

Re: Question About Air Volumes...

01/10/2011 2:38 PM

Your logic is right on! Equip the exhasut fan with a variable speed drive (VFD) and a controller with a differential pressure sensor sensing both the well and atmospheric pressures and you're set to go. Using the VFD instead of a controlled damper in the exhasut fan discharge will pay for itself with the savings in energy consumed.