Anonymous Poster

DSDR

01/08/2011 10:00 AM

why do we mention frequency and voltage in case of power distribution specification?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: dsdr

01/08/2011 10:06 AM

Because that makes more sense than mentioning air speed and altitude.

Is there really a question here?

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#2

Re: DSDR

01/08/2011 3:47 PM

Because :-

  1. Voltage too low - customers lamps go dim etc.
  2. Voltage too high - customers lamps go very bright then fail etc.
  3. Frequency too low (voltage normal, or worse, high) - customers' transformers overheat. Most motors run slower in proportion to frequency.
  4. Frequency too high (voltage normal, or worse, low) - Motor driven loads like fans and pumps run faster (% increase in load is twice increase in frequency e.g 5% frequency increase causes 10% load increase) and can be overloaded.
  5. Everything "AC mains" electrical you buy is designed to work at nameplate voltages and frequencies with small variation from them. If distribution voltage/frequency were not coordinated with that, many would not work well or fail quickly.
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: DSDR

01/09/2011 2:20 PM

Adjusted to be relevant to "power distribution system", meaning the ENTIRE transmission system used by utilities.

  1. Voltage too low - Nothing works, everything eventually burns up
  2. Voltage too high - Everything explodes, then nothing works
  3. Frequency too low (voltage normal, or worse, high) - ALL transformers overheat. AC motors run slower in proportion to frequency, DC power supplies may not care.
  4. Frequency too high (voltage normal, or worse, low) - Motor driven loads like fans and pumps run faster (% increase in load is twice increase in frequency e.g 5% frequency increase causes 10% load increase) and can be overloaded.
  5. Everything "AC mains" electrical you buy is designed to work at nameplate voltages and frequencies with small variation from them. If distribution voltage/frequency were not coordinated with that, many would not work well or fail quickly.
__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#4
In reply to #3

Re: DSDR

01/10/2011 4:01 PM

Entirely true. Do not search for DSDR to find where the question came from...

Reply