Droop Mode and MW Mode Selection

01/09/2011 12:16 PM

I would like to know about gas turbine operation, is it possible to have droop mode and MW mode together?

Concept: If line frequency changes then droop regulation (4% or 5%) will control and pull the MW back. At this moment, MW mode will try to match the actual MW with reference MW already set.

__________________
Shams ul Islam.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Droop mode and MW mode selection.

01/09/2011 2:53 PM
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Power-User
Engineering Fields - Petroleum Engineering - Rig Electrician United States - Member - the Oil Patch Engineering Fields - Power Engineering - Drives & Gen's Engineering Fields - Instrumentation Engineering - Drive Control Popular Science - Cosmology -

Join Date: Jan 2010
Location: Houston off/on-shore @ Oil Patch
Posts: 223
Good Answers: 2
#2
In reply to #1

Re: Droop mode and MW mode selection.

01/09/2011 4:09 PM

GA as usually msamad with generator setup reference, couldn't help with my "check the fuel filters" advice for load sharing problems with this . Much too complex to try "detrail method" for anyone as some have tried, point them in the right direction is the best. The woodward book is great.

Stay dry today,

I'm off soon to replace a bunch of GE GEM analog speed/voltage controls with new GE EGR digital control units. I bet you work with MUCH bigger stuff than this.

__________________
Why do they make manhole covers round? so they won't fall in [before asking "Who is John Galt?"]
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#3

Re: Droop Mode and MW Mode Selection

01/10/2011 5:51 AM

Yes, it is usual for Grid Codes to require a droop governor on units above a certain size. But electricity is sold on the basis of a unit declared megawatt, because the loads are megawatts and take no regard to generator capacity variation with ambient! Declared capacity may be varied "day to day" for gas turbines. The governor always operates in droop, the plant control has a slower-acting megawatt control loop, which adjusts the governor speed setting as a "robot operator" to keep the MW at target for the "run", despite frequency variations typically +/- 0.2% in UK. A GT governor will respond to frequency change with a "simple lag" response of about a second or so (depends on size and type); whilst "MW loop" would take 30s or more to correct effect of 0.2% frequency change on MW output. Consequently, governor contributes to frequency control in short term, though longer term regulation is a management operation.

You may find it useful to look at http://www.nationalgrid.com/uk/Electricity/Codes/gridcode/ where you can the United Kingdom Grid Code for generating plant 50MW or greater. There are also commercial rules for bidding and supply of electricity.

Register to Reply
Register to Reply 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

67model (1); kwcharlie (1); msamad (1)

Previous in Forum: Automation Course   Next in Forum: im in mccb
You might be interested in: Frequency Synthesizers, Power Frequency Converters

Advertisement