what mean Im in the mccb
Good Answers: 244
Re: im in mccb
01/09/2011 5:55 PM
Is it Im or Icm?
Icm = Rated short-circuit making capacity
Extract from IEC 60947-2:
4.3.5.1 Rated short-circuit making capacity (Icm)
The rated short-circuit making capacity of a circuit-breaker is the value of short-circuit making capacity assigned to that circuit-breaker by the manufacturer for the rated operational voltage at rated frequency and at a specified power factor for a.c., or time constant for d.c. It is expressed as the maximum prospective peak current.
- MS
Re: im in mccb
01/10/2011 12:13 AM
It may be the setting of magnetic trip.Then what is Ir?.
pnaban
Re: im in mccb
01/10/2011 1:30 AM
I am. I,m in mccb. That is correct.
Re: im in mccb
01/10/2011 10:08 AM
Please refer www.electrical-installation.org/lv switchgear functions and selection In-rated current Ics-rated breaking capacity Icm-rated making capacity Icu-ultimate SC breaking capacity(fault level) Icw-short time withstand current Ir(Ith)-over current Im-Short circuit current You can also find types B,C,D mcb's tripping characteristics Compare Fuses type g,a,G,M