Double Regulating Valves on Supply or Return Piping

01/10/2011 8:24 AM

Double Regulating valves provided in chilled water branch lines for balancing and achieving systems flows are sometimes seen on supply and sometimes on return piping. Is there a strong technical reason or preference for locating them on supply or return? Do these work equally well regardless of which line they are on and is balancing achievable equally well?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Commentator

Join Date: Oct 2010
Posts: 55
Good Answers: 2
#1

Re: Double Regulating Valves on Supply or Return Piping

01/10/2011 8:09 PM

Whenever possible, balance valves should be placed on the return side of coils to reduce air and noise problems. ASHRAE states that "water velocity noise is not caused by water but by free air, sharp pressure drops, turbulence, or a combination of these, which in turn cause cavitation or flashing of water into steam" (1997 ASHRAE Fundamentals Handbook, page 33.4). Compared with placement on the supply side, balance valves on the return side will reduce the amount of free air in the coil. Result is less noise and better control of the coil. Flow will be controlled using supply or return. Do what is best for your system.

Reply Good Answer (Score 3)