Cable Selection For Low Voltage Application

01/11/2011 4:10 AM

Can anyone suggest me appropriate cable for :

1. transferring 0-10 V DC to a distance of 150 meter.

2. 4-20mA current transferring for the same distance

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Cable selection for low voltage application

01/11/2011 5:38 AM

2c 0.75mm2 would do for either. This is an everyday installation in many industries.

"2 bits of wet string" would do for 4-20mA!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2
In reply to #1

Re: Cable selection for low voltage application

01/11/2011 10:45 AM

At 0.75mm2, the mechanical strength of the cable is the determining factor. Anything smaller might get damaged over those 150m, and therefore won't be worth the trouble of installing it.

As this is an analog signal, go for a screened twisted pair, with PVC/SWA/PVC overlying it for mechanical protection.

The 4-20mA won't be affected by interference and induction, which is why it is an industry standard signal; if 20mA goes in one end there's every chance of the same 20mA coming out the other....

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#3

Re: Cable Selection For Low Voltage Application

01/12/2011 2:37 PM

In both cases, the resistance of the complete cable loop must be considered. The 0.75 mm2 cable previously suggested would give a loop resistance of 65 ohms. Your signal source may not be strong enough to drive through that much burden. The source for the voltage signal would not be harmed, but the value on the receiving end would not be 0-10 volts. If the 4-20mA signal is generated by a constant-current amplifier, it will raise its output voltage in an attempt to overcome the line resistance plus the receiver load resistance (usually a dropping resistor of 250 ohms). If the source is not designed to drive through 315 ohms, it may damage itself trying.

For that distance I would use at least 2.5 mm2 twisted shielded pair cable, with the shield terminated to ground only on the source end.

__________________
Experience: The knowledge you gain just AFTER you needed it.