Testing a Motor

01/12/2011 11:57 PM

Can somebody suggest a full motor test before in can be put back in situ? Once bearings have been replaced on a 3 phase induction motor is there any recommended electrical and mechanical test that you can suggest? Currently we just do an insulation and winding resistance test.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#1

Re: motor test

01/13/2011 12:01 AM

You can for an high voltage test also..

__________________
You don't understand anything until you learn it more than one way.
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: motor test

01/13/2011 12:11 AM

Did you notice if the original bearings are electrically isolated?

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Commentator

Join Date: Jan 2011
Location: Rockhampton Queensland
Posts: 67
Good Answers: 1
#15
In reply to #2

Re: motor test

01/14/2011 6:50 AM

We don't want them above or below earth potential. after all, I hope they are stuck in an insulated end plate, and also insulated from the main rotor, otherwise the world would ...well ....explode or something...............

Has to be a problem that I have never heard of...?

but, always eager to learn.

Mark N,

__________________
I dislike "Anonymous" intensely. It is like they have something to hide? Their Cowardice.! I also dislike those Who will not help themselves, by not replying, to a civil Question.
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: motor test

01/13/2011 12:12 AM

A 24 hour "light load" test run.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: motor test

01/13/2011 1:06 AM

A "growler" test on the rotor if it hasn't been put back into the stator yet.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7
In reply to #4

Re: motor test

01/13/2011 6:28 AM

HeHe never done a Growler test since I was an apprentice!

How do you do it with a squirrel cage rotor?
(that what the OP asked)

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: motor test

01/13/2011 1:29 AM

Everything so far sounds good. Mechanically, you can also push both shaft ends up/down/left/right to check for excessive play, using a dial indicator.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster
#6
In reply to #5

Re: motor test

01/13/2011 3:42 AM

Most mechanical defects should be seen when replacing bearings, both with the condition of the bearings being replaced and the condition of the bearing landings, also the bearing fit should not be loose in some cases heat is required for fitting. When the motor is complete some lift will probably be seen on the shaft, this is determined by the size of motor and bearing type speed clearances which can be quite noticeable (high speed bearings). As suggested an unloaded test run is the best method, checking the temperature and vibration levels.

Reply Score 1 for Good Answer
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#8

Re: Testing a Motor

01/13/2011 10:00 AM

If you know the motor is intended for VFD duty, it may require specialized bearings and run testing at minimum and maximum rated speeds.

__________________
CRTL-Z
Reply
Active Contributor

Join Date: May 2009
Posts: 10
#9

Re: Testing a Motor

01/14/2011 1:27 AM

A no load current can be of help if you have previous or nameplate record of the same.

Reply
Commentator

Join Date: Jan 2011
Location: Rockhampton Queensland
Posts: 67
Good Answers: 1
#10

Re: Testing a Motor

01/14/2011 1:37 AM

I reckon you just about have it.

Q. Why did you have to replace bearings, planned maitenance.

Check that the Fitter has aligned his pump or load correctly..! If he is the man to connect up. A flexible coupling can only do so much.

__________________
I dislike "Anonymous" intensely. It is like they have something to hide? Their Cowardice.! I also dislike those Who will not help themselves, by not replying, to a civil Question.
Reply
Anonymous Poster
#11

Re: Testing a Motor

01/14/2011 2:18 AM

In case the bearing replacement is done with conventional method means that use of improper tool and not of standard bearing fitting kit , we should must check the viberation test of the motor of drive end , rear end , foundation and on the middle of motors. It will be more useful if there is the origional results for comparision , otherwise to maintain with in the standard can be checked from manufacturer .

A.K.Sharma

Reply
Anonymous Poster
#12

Re: Testing a Motor

01/14/2011 4:29 AM

there is no such full motor test, if you done insulation testing, be sure that all the wedges are properly placed, be sure also the internal connection of winding observe polarity. Now you can test the motor for proper wiring connection put a small bearing inside the motor, over the winding then energize the winding with voltage stated to its nameplate, use a motor starter so that you can jog it. Observe the the rotation of the bearing and the sound of the winding.

Reply Off Topic (Score 5)
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#13

Re: Testing a Motor

01/14/2011 4:33 AM

Windings Insulation test against the Body.

Windings resistance.

Visual Checks before replacing the bearings: Any markings on the windings indicating rubbing against the rotor before bearing replacement. These Insulation scratches might not show during testing but will develop rapidly when in use to a winding failure...

No load test run to check for vibration and bearing noise.

When connected back on the equipment, Load testing for the same as above plus current loading to compare with the nameplate and previous records if available. Monitor for temperature rise specially near the bearing housings to check the condition of the bearings and their seatings.

Finally, the Original Reason for the Failure (if early failure) must be diagnosed and corrected.

For a 3phase induction motor with squirel cage rotor, there is no Crawler test as suggested. But if the motor is of a big size (>= 10 HP) you might want to check the rotor/shaft for any play between the laminations and the shaft (none should be there) or any damages to it...

Reply Score 1 for Good Answer
Commentator

Join Date: Jan 2011
Location: Rockhampton Queensland
Posts: 67
Good Answers: 1
#14
In reply to #13

Re: Testing a Motor

01/14/2011 6:38 AM

Cheee, we realy are getting excited now.

# ea x 3 phase. the resistance is equal

Insulation >100k

Spins freely.

wire the bastard in, and switch it on.

lets not get to carried away

__________________
I dislike "Anonymous" intensely. It is like they have something to hide? Their Cowardice.! I also dislike those Who will not help themselves, by not replying, to a civil Question.
Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#16
In reply to #14

Re: Testing a Motor

01/14/2011 11:12 AM

Refer to your reply #15: YOU seem to be carried away... Bearing potential above or below ...?? exploding the motor... He will just trip his CB...

The Op is asking for advice from experience and either you help or just let it be.

Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#17

Re: Testing a Motor

01/14/2011 11:35 AM

NEMA has some very comprehensive guides for electric motors, including testing.

__________________
CRTL-Z
Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#18

Re: Testing a Motor

01/16/2011 9:14 AM

dpends upon the rating.On smaller motors IR value and simple no load running may do.On large machines u have to do additional tests suh tan Delta and compare with original test records, PI value , capcitance test and so on. Regards

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Anonymous Poster
#19
In reply to #18

Re: Testing a Motor

01/17/2011 10:45 AM

Depending on how much time you wish to spend with it,

I would look at Insulation Resistance, (Dielectric Absorption OR Polarization Index) done with DC of course.

Phase to Phase Inductance and Resistance to the microhenry/ohm.

and since the motor has been apart for bearings, Rotor Influence Check for out of roundness... done first, since the other tests will possibly polarize the rotor.

once running do the online battery as well as Vibration tests...

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#20

Re: Testing a Motor

01/17/2011 12:05 PM

"HeHe never done a Growler test since I was an apprentice!

How do you do it with a squirrel cage rotor?

(that what the OP asked)"

"...on a 3 phase induction motor"

Oops, missed that detail. <sheepish grin>

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Reply to Forum Thread 20 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (4); JRaef (2); LAA_Lucke (2); Markone (3); nesubra (1); redfred (1); TonyS (2); Tornado (1); tquad (1); Unredundant (2); vijaymail_electrical (1)

Previous in Forum: Induction Motor Design   Next in Forum: Connect 4x12v SMPS of 10amps Each in Series

Advertisement