Hi,

I would appreciate it if someone can help me out with my queries.

i am in the process of designing electrical installations for an aircraft hanger. and need to distribute a 400Hz at 115 volts supply to certain points.

due to skin effects the resistance of cable will increase and also at this frequency i know that the volt drop will increase .

my question:

what is the derating factor to use for the cables as compared to the ordinary cable ratings at 50 HZ for single cores and 4XC

Regards SAK

__________________
A wise person will understand more from a Foolish question than what a Fool will understand from a Wise Answer
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Cable Ratings

01/13/2011 10:42 AM
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2
In reply to #1

Re: Cable Ratings

01/13/2011 12:23 PM

Also, 67model gives a good explaination here:"Re: 400 HZ Aerospace Appllications" by 67model

Register to Reply Score 1 for Good Answer
Commentator
Engineering Fields - Power Engineering - Projects Engineer

Join Date: Aug 2008
Location: Tanzania- East Africa
Posts: 71
#7
In reply to #2

Re: Cable Ratings

01/15/2011 12:56 AM

thnks Lynlynch a very helpfull guide that was

SAK

__________________
A wise person will understand more from a Foolish question than what a Fool will understand from a Wise Answer
Register to Reply
Anonymous Poster
#3

Re: Cable Ratings

01/13/2011 2:19 PM

Refer the standards IEC 60228,class 5 and VDE 0295. 400Hz cable construction is different than normal 50Hz or 60Hz cable. The cable manufactured with the consideration of skin effect. Please see some 400Hz cable data.

cable selection depends on Rated voltage, Dc conductor resistance,inductance,voltage drop,current rating, conductor temperature ,ambient temperature and maximumshort circuit current.

Advice:- Please contact any manyfacturer before starting your design.

Register to Reply
Participant
United States - Member - New Member Engineering Fields - Nanoengineering - Stef's background

Join Date: Aug 2010
Location: California, USA
Posts: 2
#4

Re: Cable Ratings

01/14/2011 5:11 PM

Seconding the advice of the third reply; contact your wire/cable supplier. Most wire/cable companies have software models in their cable design which will calculate the parameters of interest and are very happy to aid in design.

Best regards,

Stef

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#5

Re: Cable Ratings

01/14/2011 5:36 PM
  1. Derating factor for a single isolated cylindrical conductor at 400 Hz can be judged from a 5% increase of resistance over DC resistance for an 0.8 cm diameter conductor. It will be less for smaller diameters.But it would be best to consult a cable manufacturer for tested ratings.
  2. Inductance of a 2 wire circuit depends mostly on the spacing D between conductors as a ratio to conductor radius r (i.e. D/r). Inductance is 0.063 + 0.46 x log (D/r) microHenries per metre. For D/r = 4, it is about 0.33 microHenry/m. The "constant" 0.063 is actually for a 7 strand conductor and falls to 0.05 for 37 strands.
  3. The inductive reactance for D/r = 4 comes out as about 1.8 mV/Amp/metre at 400 Hz. This means that for about 20 sqmm, the inductive reactance X is about twice the resistance R. At this ratio, the impedance is about 2.3 times the reactance - for bigger cables the resistance will hardly matter for volt drop, noting Z² = R² + X².
  4. For 100 amp cable rating, 1.8 mV/A/m is 180 mV/m. 3.6V drop over 20m run - about 3% of 115V.
  5. Hence over long runs, volts drop may be more important than rating reduction.
  6. Considering 4. - on a long run, multiple cable pairs in parallel may be the only way to reduce volt drop. Ring circuits may be more effective than spurs for all.
  7. I would check-up on the effect of wires in steel conduit and trunking. Even at 50 Hz wires in conduit see significant increase of S/C impedance compared to wires in non-metallic trays.
Register to Reply Score 1 for Good Answer
Commentator
Engineering Fields - Power Engineering - Projects Engineer

Join Date: Aug 2008
Location: Tanzania- East Africa
Posts: 71
#6
In reply to #5

Re: Cable Ratings

01/15/2011 12:37 AM

Thanx 67 for the reply will guide me appropriatly

__________________
A wise person will understand more from a Foolish question than what a Fool will understand from a Wise Answer
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#8
In reply to #6

Re: Cable Ratings

01/15/2011 5:20 AM

Pardon me, SAK, but I goofed on item 3 of post#5. My ancient brain pulled out the volt drop per sq. mm for 1 metre length of copper - not the loop resistance. The other bits I got from text or tables. Reactance becomes twice resistance for 50 sq.mm, so the bit about 100 Amp cable was OK. One more thing - with so much inductance drop, you can get unbalance between phases unless you use the symmetrical trefoil arrangement for 3 ph single core cables.

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (2); Anonymous Poster (1); lyn (2); SAK (2); StefanieHarvey (1)

Previous in Forum: DFIG in Windmill Technology?   Next in Forum: Bathroom

Advertisement