Pole Mounted Transformer

01/18/2011 1:47 AM

Hi

i intend connecting a pole mounted transformer in an underground network by converting a portion of the network to OHL and then back to underground cable. i intend using 4 poles for the riser poles. that means two outdoor terminations.

do i need surge divertors at both ends of the outdoor terminations(where cable meets OHL) ?

already the transformer is going to have a dedicated surge divertor.

the riser poles will be 5m apart.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: Pole Mounted Transformer

01/18/2011 9:26 AM

It is highly recommended to have surge arresters at the terminations where the underground cables connect to your overhead cables at the riser poles. The arresters at the transformer are there to protect its windings, and may not even be on all the phases (depending on the transformer connection to the line). The best place for protection is nearest to the equipment you want to protect.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Pole Mounted Transformer

01/18/2011 10:29 AM

I can't see the sense in having the two terminating poles just 5m apart. To gain enough cable length the cable needs to be cut and the poles sited far enough apart to allow the cut ends to reach the top of the poles, otherwise your going to have to have an underground joint.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Participant

Join Date: Sep 2007
Posts: 4
#3
In reply to #2

Re: Pole Mounted Transformer

01/18/2011 2:03 PM

there is going to be 2 inline joints plus 2 o/d terminations

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4
In reply to #3

Re: Pole Mounted Transformer

01/18/2011 3:26 PM

Re-think how you cut the cable, it can be done with 1 joint and the 2 pot heads. To me UG joints = problems.

PS, I trained as a jointer!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#5

Re: Pole Mounted Transformer

01/19/2011 6:13 PM

You definitely need surge arresters at both end terminations; specifically heavy duty Riser Pole that are designed to protect underground cable circuits.

Register to Reply
Member

Join Date: Dec 2010
Location: India, Gujarat, India
Posts: 6
#6

Re: Pole Mounted Transformer

01/20/2011 11:45 AM

Let me emphasize why surge arrestors are required. Normally the use of surge arrester is to protect the equipment from lightning surges.Now we put surge arrestors on overhead lines because where we find the overhead line in rural area, means no building or construction with a height more than the height of overhead line, there are more chances of lightning on that particular overhead line. That lightning surge will travel through that overhead line, which will result in conductor breakdown OR overhead line accessory failure. Now, when you use cable for feeding PMT there are no chances of travelling lightning surges through the cable.(Chances are less, when there is a shorter length of overhead, though it depends on surrounding area) Yes, it is required to provide surge arrestor before PMT. In addition to that, the earth you provide to Surge arrestor should be separate from PMT body/neutral earthing.

Register to Reply Score 1 for Good Answer
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ankitgj (1); Bluestone (1); kingsley064 (1); PeterT (1); TonyS (2)

Previous in Forum: lpg or diesel to cng conversion   Next in Forum: About Transformers Testing

Advertisement