Anonymous Poster

What Causes Under Voltage on Over Head Lines?

01/18/2011 7:29 AM

During an afternoon heavy down pour associated with Lightning and thunder storm,a percentage of housing units experienced dim lamps,while others where nomal.For sure there was an under voltage.This condition lasted for 6 hours and there after was normalised.What could have caused an under voltage in this particular situation?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#1

Re: What causes under voltage on over head lines?

01/18/2011 7:57 AM

one phase of delta side of distribution transformer might be under open circuit fault.

Reply
Active Contributor

Join Date: Jan 2011
Posts: 10
#2
In reply to #1

Re: What causes under voltage on over head lines?

01/18/2011 8:06 AM

Thanks for your response,do you mean to say that as a result of the open circuit in one of the phases,there was an inrush of current in the healthy phases thereby pushing voltage down?

Reply
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#3
In reply to #2

Re: What causes under voltage on over head lines?

01/18/2011 8:32 AM

well i am not sure about that but i guess someone more experienced will give you an explanation.I can assure you there is a solid explanation for anything happens in power systems.

Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4
In reply to #3

Re: What causes under voltage on over head lines?

01/18/2011 1:44 PM

If one phase is open on the delta primary (fuse blows, tree branch breaks wire, etc.) but there isn't a fault that trips the source's circuit breaker, the current will still flow through the delta winding from the two remaining phases, but divided and unbalanced between the windings (Draw the picture - two windings in series, in parallel with the other winding). Thus two of the 3 secondary wye windings will have a proportionally lower voltage due to the phase voltage split across the 2 series primaries. Once the utility restored the 3rd phase, it was back to normal.

This condition ("single-phasing") is particularly bad for motors, and will burn them out quickly. That is why phase imbalance protection is important on larger motors.

__________________
To get the right answers, first you need to ask the right questions.
Reply Score 1 for Good Answer
Participant

Join Date: Jan 2011
Posts: 2
#5

Re: What Causes Under Voltage on Over Head Lines?

01/18/2011 8:06 PM

will overloaded cause voltage drop?

Reply
Reply to Forum Thread 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

hithuanand (2); joanaphiri (1); PeterT (1); yushar (1)

Previous in Forum: Calculate Lux from Lumens   Next in Forum: Cutler Hammer Contactors Interrupting Rating & Drop Out Time
You might be interested in: Lamps, High Intensity Discharge Lamps, Halogen Lamps

Advertisement