Cable Sizing

01/20/2011 5:52 AM

hi,

let me suggest suitable size of cable for output of 750KVA DG Set. is 3.5 x300sqmm copper armoured xlpe 1.1KV is OK.

if not pl.suggest

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: cable sizing

01/20/2011 6:41 AM

If you do not want to do your calculation, Please ask an astrologer. He will suggest.

Register to Reply Off Topic (Score 5)
3
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: cable sizing

01/20/2011 7:32 AM

I assume that the rated voltage of the DG set is 415V. Then, the full load rated current of the DG set would be about 1043A. 300 sq.mm Copper cable's continuous current rating - under standard conditions - would be about 400A. But, then there has to be some derating as the standard conditions are not practicable. Say, you de-rate to 75%, then the practical continuous current rating of this cable is 300A. Then you need at lease three or four runs of this cable for this DG set. But, if the current is above 1000A, it is general practice to opt for bus bars rather than cables - as termination of so many runs of high cross section cable conductors in the small terminal box of tge alternator would be a cumbursome process.

Register to Reply Good Answer (Score 3)
Member

Join Date: Dec 2010
Posts: 6
#4
In reply to #2

Re: cable sizing

01/21/2011 3:08 AM

ok it is suggested by dg vendor that every phase and neutral will connect through a separate cable. i understand the current capacity of DG and cable, naturally it is not possible to connect all the cable in a cable alley. then what is ur suggestion

Register to Reply
Member

Join Date: Dec 2010
Posts: 6
#5
In reply to #2

Re: cable sizing

01/21/2011 4:06 AM

i understand ur points, it is dg vendor suggestion, he suggest 3.5 C,300sqmm copper cable for R,Y,B and neutral. the distance of DG and panel is 100 Mtr. what is ur suggestion

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6
In reply to #5

Re: cable sizing

01/21/2011 4:42 AM

Do you mean the undermentioned arrangement?

R, Y & B Cores of Cable-1 will get terminated to Terminal "R" of the generator,

R, Y & B Cores of Cable-2 will get terminated to Terminal "Y" of the generator,

R, Y & B Cores of Cable-3 will get terminated to Terminal "B" of the generator,

and the Black cores of all the three cables can be bent & terminated to the "N" terminal of the generator.

Is it your idea?

If so, I strongly suggest against it, because, in such a case, there will be severe heating of the armour of each cable and the cable insulation might damage sooner than later.

Better go for bus bars.

Else, if cables are unavoidable go for spreader links & a cable adaptor box.

Register to Reply
Member

Join Date: Dec 2010
Posts: 6
#7
In reply to #6

Re: cable sizing

01/21/2011 6:19 AM

No, the proposal is as under:

R, Y , B & N Cores of Cable-1 will get terminated to Terminal "R" of the generator,

R, Y , B & N Cores of Cable-2 will get terminated to Terminal "Y" of the generator,

R, Y , B & N Cores of Cable-3 will get terminated to Terminal "B" of the generator,

R, Y , B & N Cores of Cable-4 will get terminated to Terminal "N" of the generator,

I may go for bus bar what the distance between DG and Panel is 100Mtr.Approx

Lets suggest

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8
In reply to #7

Re: cable sizing

01/21/2011 7:22 AM

That means 1050 sq.mm of copper conductor each for the three phases and for the neutral too. Still, the phase conductor cross section is a weebit undersized, I feel, what with three/four conductors grouped together.

Moreover, why should the neutral require 1050 sq.mm? Is it not a waste of money?

If the distance is 100M it is all the more reason to go for bus bar, because the voltage drop in cable might be more than that in a bus for the same distance.

If due to some other reason, you cannot go for bus bar, then I suggest that you go for Copper Spreader Links emanating from the generator terminal box connnected to a more voluminous Cable Adapter Box, and connect as below:

R cores of Cables 1 to 4 to terminal R

Y cores of Cables 1 to 4 to terminal Y

B cores of Cables 1 to 4 to terminal B

Blk. cores of Cables 1 to 4 to terminal N

Please care to have enough splitting & bending space in the adapter box.

Register to Reply Score 1 for Good Answer
Commentator
Engineering Fields - Power Engineering - Projects Engineer

Join Date: Aug 2008
Location: Tanzania- East Africa
Posts: 71
#3

Re: Cable Sizing

01/20/2011 9:38 AM

i will go with expert 65. enough allowance has been made for distance and installation factor

__________________
A wise person will understand more from a Foolish question than what a Fool will understand from a Wise Answer
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - Hentoyk Philippines - Member - BRUTUS Saudi Arabia - Member - Brutus United Arab Emirates - Member - Brutus

Join Date: Aug 2009
Location: Gulf Region, IIEE_CRCSA
Posts: 113
Good Answers: 2
#9

Re: Cable Sizing

01/24/2011 12:24 AM

My opinion is max. current carrying capacity of 300mm.square is 559A CU/XLPE/PVC/SWA direct laid in the ground derating factor is 0.82(as adoptable in Saudi Electric Co-SCECO. KSA). In most stand-by power plants here in our area we do not recommend multi-cores conductor power cables either installed in cable trays or in cable trench. Power Plants or MV 132/13.80 Kv sub-distribution substations, we recommend the power cables between the gen-sets via ATS/MTS to MDB are single core cables. The advantage is easy to terminate, cable heat is minimal compare to multi-core cables. So your cable size is okey as you determined in your calculation to be 1,043amp. therefore 559x0.82 = 458amp net capacity of 300mm.sq XLPE cable. Then you need 3x300mm.sq to hook up in three terminals of gen.set as RYB or you can use neutral at full-size + 95mm.sq earthing. Then allow 25% for inrush/transient current will be 1,043ampx1.25=1,304 amp so your cable is 458x3= 1,374 amp greater than 1,304 amp(cables is safe)

__________________
If there is a will... there is a way... No pain / No gain.
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (3); GULSHAN KUMAR (3); hentoyk (1); SAK (1)