Good Answers: 3

Drop in P.F & Error in Power Calculation

01/21/2011 3:33 PM

How to reduce error in power calculation (Induction motor) due to change of Power Factor?

what is the reason in this case of P.F drop?

Here I am giving comparison of both types of measurement from

1. Energy Meter
2. Theoritcal Calculation of Power by Getting valu from C.T

At the time of measurement Load was 81 % (from C.T)

Compressor Motor: 250 KW, 400 V, 50 Hz, D, 440 A, P.F 0.86

1.Power Calculation from Energy meter:

Voltage = 392 V
Current = 346 A
P.Factor= 0.824
Power = 194.1 KW


2.From CT value in MCC (Simocode):

According to C.T, current is 356.4 A (81 %)

Voltage = 392 V
Current = 369.6 A
P.Factor= 0.86 (Taking NamePlate P.F = 0.86 )
Power = 208.1 kW

Error in both reading is 6.72 %

The Substation have 7 no of compressors each having 250 KW induction motor.In the Substation Capacitor bank Controller (BK-12) shows power factor of 0.95. We Put energy meter in MCC at the output of magnetic contactor. There Power Factor according to that meter was 0.824.

Motors have Loads in the range of 80-90 %. Other Loads are Lighting & Heating elements.

The question I want to ask that why power factor drop down to 0.824 as motor power factor is 0.86?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Associate

Join Date: Aug 2010
Location: bhubaneswar
Posts: 34
Good Answers: 1
#1

Re: Drop in P.F & Error in Power Calculation

01/22/2011 3:01 AM

Hi,

According your given data, You are are only using the power 80% approx of full load (calculated by energy meter),but your motor ratting is given at full load.the power factor is calculated at full load.And if you are calculating the theoritical practical some difference will occurs obviously.Because some other factor is also affecting the parameter that's why power factor will change.

Eg: - Impedance of load is calculate by formula in series circuit

Z= sqroot(R^2 + ( WL-1/WC)^2)

OR

z=sqroot(R^2 + (XL - Xc)^2)

In this equation only XL-XC is responsible for power factor for lagging of leading.

thanking you.

Register to Reply Good Answer (Score 2)