We are using VSDS drive ACS-1000 ....Big cabcity compressor..whil starting compressor relay indication will appear MCB trip...DRIVE TRIPPED....we changed all importent cards...we still did not found probulem ...what is the solution
Is the compressor "unloading" system being properly activated if it has one to lessen the staring torque? If this is a rotary or centrifugal it generally has an inlet control valve or if a recip a valve unloader system. Staring current on compressors can be extremely higher than most other applications and this starting current must either be minimized through unloading or by-passing or you must increase the current limiters capacities or overloads for the necessary amount of time.