Generator Selection - Three Phase Diesel Generator of 10KVA

01/25/2011 7:19 AM

Hi

I have a three phase diesel generator of 10KVA, what is the maximum load this generator is apable to supply. All the loads in the house are single phase and the waltage total is about 18kW, will this generator be capable of supplying power to the house?

Regards

D.D.Mtonyole

Register to Reply
Pathfinder Tags: Generator size
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Generator Selection - Three Phase Diesel Generator of 10KVA

01/25/2011 7:46 AM

10KVA DG normally have an efficiency of 80% and it is designed to work under 120% of its capacity so 10X.8X1.2=9.6KVA -Hit

Register to Reply
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Generator Selection - Three Phase Diesel Generator of 10KVA

01/25/2011 8:41 AM

In a word no. The wiring would be a nightmare as the loads would have to be split across the three phases to balance the loading.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 2)
Anonymous Poster
#3

Re: Generator Selection - Three Phase Diesel Generator of 10KVA

01/25/2011 9:32 AM

Use SCADA system with a proper load shedding scheme to control the total load always less than 9KVA. BMS system also can be used. Dear Gurus, please propose a load shedding scheme.

Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Generator Selection - Three Phase Diesel Generator of 10KVA

01/25/2011 2:00 PM

If the generator is rated at 0.80 power factor, it can supply 8kw continuously, and maybe a bit more if intermittent.

The 18kw sounds like the total connected load, not all of which is likely to be running at once. Maybe you can find some ways to ensure that only 8kw is running at the same time. You also need to figure out how to distribute your loads among the three phases.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#5

Re: Generator Selection - Three Phase Diesel Generator of 10KVA

01/25/2011 11:21 PM

My personal response would be to sell this and buy a 10KW single phase 240/120 Diesel generator to run your entire house on when the utility is down. Although I can run a 3200 Sq Ft house on a 6.3KW including the washer/dryer, furnace, all lights and more importantly all our computer equipment. Stove is Gas so eating is taken care of. All lights are energy efficient too. For you to try to use the 3 phase unit. Way too much wiring involved to do so plus the disconnects. Fogetaboutit. Sell it. Go simple. KISS method

__________________
"Real Bass Players" do not use picks
Register to Reply
Anonymous Poster
#6

Re: Generator Selection - Three Phase Diesel Generator of 10KVA

01/25/2011 11:49 PM

Yes, you must be VERY careful in assigning loads to each phase, PLUS having to increase the return buss size (Netural). Having bee burned, and old ee showed a easy way to just string some 100watt lights to the system to balance most of teh systems. however, the inrush current on fridges,etc played old harry with it. put it a UPS type system to then allocate the power as needed. that's how i see it.....

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7

Re: Generator Selection - Three Phase Diesel Generator of 10KVA

01/26/2011 12:23 AM

It depends upon the diversity factor(whether all the loads are connected at the same time)

__________________
pnaban
Register to Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#8

Re: Generator Selection - Three Phase Diesel Generator of 10KVA

01/26/2011 1:12 AM

Another solution to use the generator is to put a three phase rectifier with single phase inverter. For this power the cost would probably be higher than buying another generator.

__________________
The time is ......now
Register to Reply
Participant

Join Date: Jan 2011
Posts: 4
#9

Re: Generator Selection - Three Phase Diesel Generator of 10KVA

01/27/2011 11:46 AM

10 kVA generator can feed 10kw unity power factor loads.

if your loads not unity power factor (.8 )for exapmle the generator can feed u by .8 *10

which is 8 kw

the other important point u have to take into your consideration a diversity factor in your housee where not all devices works at same time . for example it may be 0.6 so your maximum load will be 0.6*18=10 kw

Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); engmaher2005 (1); Jimh77 (1); nikolay (1); pnaban (1); TonyS (1); Tornado (1)

Previous in Forum: Electrical Panel Board   Next in Forum: ELCB

Advertisement