Over Heating 1000KVA Alternator

01/25/2011 2:47 PM

Dears,

In my new company i noticed one old Cummins generator of 1000KVA(50Hz 4pole) is getting over heated(65degrees) on its alternator(Stamford) side just by 5 mins no load running. I suspected the winding first and did rewinding, but problem remains.

Tried by replacing AVR(MX321), no use.

Upon investigation found that AVR output (at X-XX) are 30 VDC (for terminal voltage of 415V). Tried with 12V DC external excitation after removing AVR completely, alternator not getting heated, but terminal voltage comes only 360V.

What could be the problem? Is 30 V DC excitation is very high? On a similar Generator I found it is only 11.8V DC.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Jul 2009
Location: chennai, India
Posts: 55
Good Answers: 1
#1

Re: Over Heating 1000KVA Alternator

01/26/2011 2:01 AM

Use Thermo vision camera to identify the real source of heat.

Suppose the defect is in the core , it will be identified.

Thorough testing can lead to identify the currect defect

Best wishes

__________________
There is nothing either good or bad, only thinking make it so -
Register to Reply Score 1 for Good Answer
Anonymous Poster
#4
In reply to #1

Re: Over Heating 1000KVA Alternator

01/26/2011 10:24 AM

Dear,

The 65 degree centigrade i got by IR gun thermometer.

Thanks for comment

Register to Reply
Member

Join Date: Jan 2011
Posts: 8
#2

Re: Over Heating 1000KVA Alternator

01/26/2011 4:21 AM

The temperature you described is I suppose to be 65 degrees Celsius. But this is the temperature measured on the surface of the alternator. But in the nameplate, the 65degrees temperature rise is based on the temperature rise which is based on the insulation class of the equipment. Now if the ambient temperature is 30 degrees , then you add this you have 95 degrees. If you can still touch the surface then it is still quite alright.

Now, since you already had it repaired, then it is assumed that it is clean already. So no issue on ventilation and air cooling.

The problem may be elsewhere. Do you have harmonics issue which can be the culprit?

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jan 2011
Posts: 12
Good Answers: 1
#5
In reply to #2

Re: Over Heating 1000KVA Alternator

01/26/2011 10:30 AM

This particular gen set was H class before rewinding and now it is F Class. But I afraid the temp may rise beyond that(65 DC) if loaded!

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#3

Re: Over Heating 1000KVA Alternator

01/26/2011 8:40 AM

65 degrees where?? Cooling air exit? Winding buried sensor? Rotor?

Did you rewind stator or rotor? High field current to get normal volts off-load seems like rotor problem at first glance.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jan 2011
Posts: 12
Good Answers: 1
#6
In reply to #3

Re: Over Heating 1000KVA Alternator

01/26/2011 10:34 AM

65 degrees on the alternator body, and also it is not uniform.. I used IR camera for temp reading.

The rewinding was done only on the Stator.

Also please be informed that this generator is using for stand-by support.

Thanks for Comments..

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#8
In reply to #6

Re: Over Heating 1000KVA Alternator

01/26/2011 1:17 PM

Since the excitation voltage seems to you higher than similar genset (30V instaed of 11.8V ??), then I would check the Exciter winding at the end of the alternator. If the higher temperature is measured in that area of the body, then more confirmation to check it.

I hope this will help.

Register to Reply
Active Contributor

Join Date: Jan 2011
Posts: 12
Good Answers: 1
#9
In reply to #8

Re: Over Heating 1000KVA Alternator

01/28/2011 2:58 AM

Exciter (PMG) stator winding was checked for continuity (resistance values) and found ok. Also the out put from PMG are also balanced and within limit as per the manufacturers document (180V)

Register to Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#7

Re: Over Heating 1000KVA Alternator

01/26/2011 11:28 AM

You may like to run the generator at no load and monitor the temperature of same point (which has 65 degree rise). If this point still attains high temperature, then it is most probably due to core short. In that case you may like to perform ELCID test and locate the shorted core packet and attempt to repair the same.

If the temperature rise is not high, then you may perform short circuit run from reduced circulating current and then go on increasing the current till limiting temperature is reached. If it is at reduced load then there is problem with cooling of the generator.

Register to Reply
Active Contributor

Join Date: Jan 2011
Posts: 12
Good Answers: 1
#10
In reply to #7

Re: Over Heating 1000KVA Alternator

01/28/2011 3:03 AM

I also suspect the core short here. But expert comments were that is a very rare chance. And also the repair will be very costly. Thats why trying to eliminate other probable chances.

Now the only point remaining is rotating diode assy. As it is very within the alternator i couldnt do that till now. What is the chances for diode fault in this case?

Register to Reply
3
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#11
In reply to #10

Re: Over Heating 1000KVA Alternator

01/28/2011 4:44 AM

If you were able to check the exciter output, 3 phase delta windings, why not check the diodes at the same time? The exercice is done with the alternator at stand still, and by reaching the terminals of the exciter rotor windings, you are at the diodes.

In any case, if the AVR is having to deliver 30V instead of something near 12V as you have said, then it means that the exciter needed this extra voltage to produce more current into the main field (main rotor), or the necessary current required to obtain the set voltage.

In the latter case, the extra current is the one heating the area you are looking at. If the main rotor field and the exciter + diodes are healthy, the extra current would boost the output voltage high!

If the main 3phase stator winding has a fault internally, this will develop fast and it would have been already obvious.

If possible, it will be cheaper and easier to remove the exciter at the end, and give it a good check outside the unit. It is even cheaper to rewind its rotor than taking the chance of medling with the main windings: but 1st try to check the diodes. Look for damged OPEN circuit diodes.

Register to Reply Good Answer (Score 3)
Active Contributor

Join Date: Jan 2011
Posts: 12
Good Answers: 1
#12
In reply to #11

Re: Over Heating 1000KVA Alternator

01/28/2011 10:27 AM

Thanks LAA Lucke for comment,

In this case exciter rotor widing are not accessible(correct me if I am wrong). At the non driving end of the genset there is a cover and by opening it the PMG exciter is visible. But only terminals are those of stator (three cables) where I measured the out put of exciter (180V).

I can see the diode assy thru the main alternator terminal box, but being very within, not accessible. Any way if need to test it I need to remove the Alternator from the engine. I couldnt check this when I removed for rewinding.

Yesterday I did a lamp test on AVR as said in the Stamford mannual and found the AVR is healthy.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#14
In reply to #12

Re: Over Heating 1000KVA Alternator

01/28/2011 1:02 PM

The main exciter: (1) stator field winding , (2) rotor winding, (3) the rectifierbridge diodes assembly.

The AVR can be OK. The problem is that if the main exciter has a problem in any of its 3 components, it will start to compensate by supplying more current into the stationary exciter field in order to generate a higher voltage in the exciter rotor windings and maintain the same required current into the MAIN alternator rotor field and thus the maintain the Main Output Voltages.

The 1st item: Exciter Field winding should be accessible, but apart from visual or obvious leak to the body, it is difficult to realise any minor faults within. But on the long run, the winding will deteriorate relatively fast while in use.

The exciter rotor windings and the diode assembly will need physical checks and cannot be checked without removing them out.

If the Main Alternator Rotor Field was faulty, the fault would snowball quickly when running and more so if loaded.

Your best bet is to remove the Alternator and get access to the internals: Exciter windings and diodes.

If you can remove the alternator and slide out the stator body, that will be the easiest way to reach all the components for examination without removing them from the rotor shaft. But I think that you should know or maybe have some manual with instructions.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jan 2011
Posts: 12
Good Answers: 1
#13
In reply to #11

Re: Over Heating 1000KVA Alternator

01/28/2011 1:01 PM

Hi,

Let me clear one thing, I could check only PMG, not exciter. The exciter stator terminals coming to AVR are checked for correctness of resistance, its ok. To check the exciter further or to check rectifier I need to ditach Alternator again.

Register to Reply
Associate

Join Date: Dec 2009
Location: Kota Kinabalu, Malaysia
Posts: 39
#15

Re: Over Heating 1000KVA Alternator

12/14/2011 9:55 AM

hi guys... I'm also facing the same problem.... power g did u solve your problem and what actual the problem...

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#16
In reply to #15

Re: Over Heating 1000KVA Alternator

12/14/2011 5:27 PM

PowerG may not be checking this thread any more. If you click on PowerG's name (bold text) in his post, you will go to a screen which has "Send PowerG a message" button.

Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!