Breaker Trips Range

01/26/2011 12:24 AM

I have doubt regarding breaker,when will 100A breaker will trip on,each phase current beyond the limit of 100Amps(100*3=300Amps) or total current beyond 100Amps(100/3=33.33A)

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Breaker trips range

01/26/2011 12:32 AM

It goes by the current in each phase (or the the current in the maximum-current phase). The second example of 33.33 per phase will not trip the breaker.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster
#2

Re: Breaker trips range

01/26/2011 2:09 AM

A breaker has different tripping characteristics based on short time, long time, instantaneous and ground fault with respect to the current.

Register to Reply
Member

Join Date: Jan 2011
Posts: 8
#3

Re: Breaker trips range

01/26/2011 4:30 AM

Simply put, a 100A Trip breaker, will start to open when it is experiencing more that 100Amps on any of its phase or wire connected to it.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Breaker Trips Range

01/26/2011 10:51 AM

There is nothing in a standard thermal magnetic circuit breaker capable of performing math*...

Each phase has it's own current sensing device. If the breaker says "100A thermal trip" that means that each current sensing device is calibrated to trip at 100A or more (sort of, we won't go into pick-up points etc. for this discussion).

If any one of the three (or 2) sensing elements in the poles sees a current that exceeds its threshold, the element activates the tripping mechanism and opens all poles.

* That said, it doesn't actually matter anyway. 100A through a 3 phase breaker is not 3 x 100A, it is still referred to as 100A. Common misconception.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply