Correlating Ingress Protection (IP) and Explosion Protection (EP)

03/29/2007 9:56 PM

Dear friends,

I would like to know info on the correlation between Ingress protection & hazardous explosion protection. I understand ingress protection for an equipment/apparatus is against solid/dust ingress and water/liquid ingress whereas explosion protection for the same equipment/apparatus is based on the hazardous area classification. It seems ingress protection & explosion protection are independent! Is there any correlation between ingress protection & explosion protection?

For example, what is the minimum IP rating required for an Ex e certified equipment? Is there any such requirement? If yes, what about min. Ip rating required for Ex d, Ex i, Ex n, Ex o, Ex p .....? If no, please explain

thanks & regards

Mani

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Manufacturing Engineering - United Kingdom - Member - Get things done!

Join Date: Jul 2006
Location: East Anglia, UK
Posts: 2003
Good Answers: 3
#1

Re: Correlation between Explosion Protection (Ex) & Ingress Protection (IP)

03/30/2007 3:12 AM

Complicated area mate. Your best bet is to google DSEAR (Dangerous Substances and Explosive Atmospheres), these are the regulations we have to comply to. You can get some good guidance. It sounds like you need to rate you equipment into zones, thats the easy part.

__________________
'The truth is out there' The lies are in your head.
Register to Reply
Participant

Join Date: Mar 2007
Posts: 4
#2
In reply to #1

Re: Correlation between Explosion Protection (Ex) & Ingress Protection (IP)

03/30/2007 9:36 PM

Thanks for your response, mate. I too agree with you that they are regulations & we have to comply. But I strongly believe there should be a correlation as it seems quite logical. Let us discuss on the following example (Pl correct me if I'm wrong)

For example, let us consider an example of an electrical equipment with explosion protection Ex d and ingress protection IP20. As we know, IP20 rating means the equipment is protected against ingress of solid objects of size of 12.5mm & above and not protected against water ingress. Not protected against water ingress can be considered as not protected against ingress of gas! (i.e. if water can go in, why not gas can go in?!) If gas can go into an electrical equipment, ultimately the probability for explosion exists.

So, the conclusion is IP20 is not sufficient for an Ex d rated electrical equipment! The question on minimum IP rating for an Ex certified equipment and existence of a correlation between Ex & IP ratings arises here.

Can you please clarify on the subject as I'm confused?

Register to Reply
Anonymous Poster
#3
In reply to #2

Re: Correlation between Explosion Protection (Ex) & Ingress Protection (IP)

03/31/2007 1:42 AM

Exp proof is not necessarily water proof. Before we came up with the USA NEMA 4/7 rating all we had was NEMA 7 which is an indoor rating. Many NEMA 7 devices installed on outdoor switchracks invariably had water entry problems. Exp proof means that the explosion is contained within the enclosure, hence the wide flanges on that type of equipment. The idea is that the wide flanges would provide a flame path to adequately vent the explosion but that the flame would be sufficiently "cooled" by the time it got to the outside of the enclosure so as not to propagate the explosion to gases outside of the enclosure. Or at least that's the theory.

Clear as mud right?

Register to Reply
Participant

Join Date: Mar 2007
Posts: 4
#4
In reply to #3

Re: Correlation between Explosion Protection (Ex) & Ingress Protection (IP)

04/01/2007 8:58 PM

Dear Guest,

Yes, I understand/got your point. Thanks for the explanation. But, still I want to know whether there is any minimum IP rating requirements for an Ex certified electrical equipment.

Can you clear my doubt, please?

Register to Reply
Guru
Belgium - Member - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Aug 2006
Location: Glabbeek, Belgium
Posts: 1480
Good Answers: 28
#5
In reply to #2

Re: Correlation between Explosion Protection (Ex) & Ingress Protection (IP)

04/02/2007 4:22 AM

EX d has no protection against gas ingress. It is designed to keep the eventual explosion inside the box and to limit the rise in temperature on the outside.

To release the pressure due to an internal explosion, they have holes that let the gases cool before they reach the outside of the box.

__________________
"Here we are now, entertain us"
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #2

Re: Correlation between Explosion Protection (Ex) & Ingress Protection (IP)

04/02/2007 5:19 AM

"So, the conclusion is IP20 is not sufficient for an Ex d rated electrical equipment! "

Wrong way round. Ex d rated equipment will have an IP rating typically of 55 or greater. Just because a piece of equipment has a high IP rating does not make it Ex d. For example, IP68 equipment need not be Ex d rated, as the flame path may be too short and the case not substantial enough to withstand and contain an internal explosion.

Ex i equipment need not have an IP rating; provided they are fed from an approved barrier, two bare conductors forming a switch would be acceptable as "simple apparatus".

Ex e would typically have an IP rating of 55, though it is not a requirement.

Ex o and Ex q, well there one goes...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#7
In reply to #2

Re: Correlation between Explosion Protection (Ex) & Ingress Protection (IP)

04/02/2007 2:46 PM

Never try to apply logic to regulations. Regulations are completly independant of logic.

Register to Reply
Guru
Belgium - Member - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Aug 2006
Location: Glabbeek, Belgium
Posts: 1480
Good Answers: 28
#8
In reply to #7

Re: Correlation between Explosion Protection (Ex) & Ingress Protection (IP)

04/03/2007 3:50 AM

This is not completely true.

But if you read an actual regulation you see only the result of logics: the logics are in the history and preliminary work.

But as stated before: at one moment we invented the accountant (we are still looking for the engineer who did this) and the un-logical exceptions entered the system.

There is no correlation between IP and EX, for this the NEMA classification is better: an un-logical list. If you find a new way that is not in the list and you prove the usefulness they just add it. With the IP system you can't distinct it.

__________________
"Here we are now, entertain us"
Register to Reply
Member

Join Date: Nov 2014
Posts: 5
#9

Re: Correlating Ingress Protection (IP) and Explosion Protection (EP)

02/11/2015 1:38 AM

Refer for more details Electrical Engineering

Ingress Protection (IP) ratings are developed by the European Committee for Electro Technical Standardization (CENELEC) (NEMA IEC 60529 Degrees of Protection Provided by Enclosures - IP Code), specifying the environmental protection the enclosure provides.

The IP rating normally has two (or three) numbers:

  1. Protection from solid objects or materials
  2. Protection from liquids (water)
  3. Protection against mechanical impacts (commonly omitted, the third number is not a part of IEC 60529)

Example - IP Rating

With the IP rating IP 54, 5 describes the level of protection from solid objects and 4 describes the level of protection from liquids.

An "X" can used for one of the digits if there is only one class of protection, i.e. IPX1 which addresses protection against vertically falling drops of water e.g. condensation..

IP First number - Protection against solid objects

0No special protection
1Protected against solid objects over 50 mm, e.g. accidental touch by persons hands.
2Protected against solid objects over 12 mm, e.g. persons fingers.
3Protected against solid objects over 2.5 mm (tools and wires).
4Protected against solid objects over 1 mm (tools, wires, and small wires).
5Protected against dust limited ingress (no harmful deposit).
6Totally protected against dust.

IP Second number - Protection against liquids

0No protection.
1Protection against vertically falling drops of water e.g. condensation.
2Protection against direct sprays of water up to 15

o from the vertical.

3Protected against direct sprays of water up to 60

o from the vertical.

4Protection against water sprayed from all directions - limited ingress permitted.
5Protected against low pressure jets of water from all directions - limited ingress.
6Protected against temporary flooding of water, e.g. for use on ship decks - limited ingress permitted.
7Protected against the effect of immersion between 15 cm and 1 m.
8Protects against long periods of immersion under pressure.

IP Third number - Protection against mechanical impacts (commonly omitted, the third number is not a part of IEC 60529)

0No protection.
1Protects against impact of 0.225 joule
(e.g. 150 g weight falling from 15 cm height).
2Protected against impact of 0.375 joule
(e.g. 250 g weight falling from 15 cm height).
3Protected against impact of 0.5 joule
(e.g. 250 g weight falling from 20 cm height).
4Protected against impact of 2.0 joule
(e.g. 500 g weight falling from 40 cm height).
5Protected against impact of 6.0 joule
(e.g. 1.5 kg weight falling from 40 cm height).
6Protected against impact of 20.0 joule
(e.g. 5 kg weight falling from 40 cm height).
Register to Reply
Register to Reply 9 comments