Running Different Cross Section Busbars For Phase

02/02/2011 2:07 AM

Greetings to all

Can we use different cross sectioned busbars in phase?

Example:

For 800Amps ACB shorting, we use 40X10 al. bb of 2runs or some times 50x10 al.bb of 2runs. Instead can we use 50x10 & 50x6 al.bb for each phase?

Is there any disadvantage of using these kind of constructions? Please clarify?

__________________
Prem
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Running Different cross section busbars for phase

02/02/2011 5:45 AM

There could be unequal distribution of currents in these bus bars and the associated effects.

Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Running Different cross section busbars for phase

02/02/2011 5:48 AM

Can you please detail what are all those effects can be...?

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #2

Re: Running Different cross section busbars for phase

02/02/2011 6:13 AM

Different temperature rise, different thermal expansions, different forces, etc.

Register to Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#4

Re: Running Different Cross Section Busbars For Phase

02/02/2011 1:01 PM

At the ACB terminals standard practice is to exactly match the bus bar width to that of the terminals width.

(a) There is not enough clearance to accomodate a larger width bus bar at the ACB terminals.

(b) A smaller width bus bar will be a source of heating at the point of contact with the breaker terminals.

Thickness of the bus bars only can be increased or decreased to cater required current.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Anonymous Poster
#5

Re: Running Different Cross Section Busbars For Phase

02/03/2011 2:00 AM

Similarly, Please be aware that power supply cable wires with defferent line length will create phase imbalance and wire overheating.

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#6

Re: Running Different Cross Section Busbars For Phase

02/03/2011 8:24 PM

prems4573,

The brief answers from electricalexpert65 are, in my opinion, correct. I am assuming that this is an AC application. I have been thinking about this before continuing--the only way to verify the suitability of this arrangement would be to do tests with an actual layout of the unequal bus bars. Certainly this would be required to pass short circuit withstand qualifications. Good luck.

--JMM

Register to Reply
Commentator

Join Date: Jun 2010
Posts: 75
#7

Re: Running Different Cross Section Busbars For Phase

06/01/2011 6:07 AM

Theoretically, you can design such a bus bar system, but practically it will be difficult needing extra engineering effort in terms of travel and termination of such a bus bar system through a given switchgear. Moreover, both sizes (particularly the smaller size) must meet short circuit withsatnd capability criteria.

BB Raina

Register to Reply
Register to Reply 7 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); BB Raina (1); electricalexpert65 (2); jmueller (1); mountk2 (1)