Anonymous Poster

MCB Construction

02/02/2011 1:43 AM

What is 3K,6K,10K in the case of MCB .What is the factors depending them.

SA

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: MCB CONSTRUCTION

02/02/2011 5:57 AM

Please study these data a little more carefully. They are not 3K, 6K & 10K. They are 3kA, 6kA & 10kA respectively. They are the breaking capacities of the MCBs. It implies the maximum amount of current that the MCB can safely break (or open) without causing any damage to itself or to the installation or to the operator.

The selection depends upon the maximum fault level at the point of installation of the MCB.

Reply Good Answer (Score 2)
Anonymous Poster
#2
In reply to #1

Re: MCB CONSTRUCTION

02/03/2011 12:29 AM

WHAT FACTORS DEPENDING THEM ?

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #2

Re: MCB CONSTRUCTION

02/03/2011 1:54 AM

The only factor is the fault current at the point of installtion of the MCB. You should know how to calculate fault currents at various points in the network. Then only you can select the breaking capacity of the MCBs correctly.