I have connected the power supply for 8 buildings , Each 8 storey. I found common problem in all of them. if I plug any appliance to power supply in any socket in the building , a high voltage can be measured between the the equipment body and the earth terminal. it varies between 50 volts for digital receiver and 100 volt for the TV. In the same time I checked the voltage between the neutral and earth in the DB it shows zero.
In the LV panel( main Panel is also zero) ,,, in the socket before connecting any appliances , it shows zero as will.
the earthing system is ok< less than one ohm < . polarity found ok. I link the neutral with the earth bar in the main lv panel and still I have the same issue.
I found that the star point of the transformer ( which is in the AUTHORITIES side) is not connected to earth which gives flouting neutral in the system, this may be the reason. But on the other hand I have isolated one of the buildings from the substation power completely and started the standby generator. The same problem again appeared. The earthing resistance is less than 0.5 ohm
This is the first time I face the same problem and I need your advice
Thanks and best regards