how to calculate KVA, when the current per each phase is 200amp at 440volts for three phase circuit breaker or what size of generator is needed for such informations above
I try to work it at.............v x I x pf [0.8 or 1.732] / 1000======457KVA
v----Volt generated
I-----Current or Amperage
Pf----Power factor of load
440 x [200 x 3phase] x 1.732 /1000
457.248amp
I am just confused, am I correct, or please help over this
India - Member - New Member
Good Answers: 164
Re: Find KVA
02/07/2011 6:08 AM
kVA = √3 * V *I
kW = √3 * V * I * Cosφ = √3 * kVA
Re: Find KVA
02/07/2011 6:13 AM
So Cosφ = √3 ?
Good Answers: 164
Re: Find KVA
02/07/2011 6:24 AM
OOPS! never post when sleepy
Sorry OP, kW = Cosφ*kVA
Re: Find KVA
02/07/2011 6:14 AM
You do not use the power factor in calculating KVA. When you use the power factor your calculating the KW.
Re: Find KVA
02/07/2011 6:26 AM
Cosφ = KW/KVA
Good Answers: 181
Re: Find KVA
02/07/2011 6:54 AM
A x V x √3 x 3 / 1000 = KVA
KVA x Pf = KW
Re: Find KVA
02/07/2011 8:33 AM
KILOWATT (kW) = VOLTS x AMPERES x POWER FACTOR x 1.73
1000
To Convert Between kW and kVA
kW to kVA kW / .85 = SAME VALUE EXPRESSED IN kVA
kVA TO kW kVA * .85 = SAME VALUE EXPRESSED IN kW....
There are no shortcuts on the road to a great experience.
Re: Find KVA
02/07/2011 12:49 PM
Yes, OK. Do turn off Caps Lock next time, eh?
Re: How to Find KVA
02/08/2011 12:44 AM
For sizing genset,kVA is not enough.You should know the pf of load to find kW of engine. PF varies with current or load. During starting of large motor across the line pf will go down to even 0.3 due to 6times FLA drawn.Voltage/Frequency drop should be within limits at generator terminals as well as motor terminals.
pnaban
Re: How to Find KVA
02/08/2011 10:41 AM
if you use
457.248amp
you only know kVA of Load, you don't know kVA of general
Good Answers: 11
Re: How to Find KVA
02/08/2011 1:19 PM
When using line to line voltage
kVA=ExIx1.732/1000
440x200x1.732/1000=152.4 kVA