How to Find KVA

02/07/2011 5:38 AM

how to calculate KVA, when the current per each phase is 200amp at 440volts for three phase circuit breaker or what size of generator is needed for such informations above

I try to work it at.............v x I x pf [0.8 or 1.732] / 1000======457KVA

v----Volt generated

I-----Current or Amperage

Pf----Power factor of load

440 x [200 x 3phase] x 1.732 /1000

457.248amp

I am just confused, am I correct, or please help over this

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Find KVA

02/07/2011 6:08 AM

kVA = √3 * V *I

kW = √3 * V * I * Cosφ = √3 * kVA

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#2
In reply to #1

Re: Find KVA

02/07/2011 6:13 AM

So Cosφ = √3 ?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4
In reply to #2

Re: Find KVA

02/07/2011 6:24 AM

OOPS! never post when sleepy

Sorry OP, kW = Cosφ*kVA

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Active Contributor

Join Date: Nov 2010
Location: Ireland
Posts: 15
#3

Re: Find KVA

02/07/2011 6:14 AM

You do not use the power factor in calculating KVA. When you use the power factor your calculating the KW.

Register to Reply
Active Contributor

Join Date: Nov 2010
Location: Ireland
Posts: 15
#5

Re: Find KVA

02/07/2011 6:26 AM

Cosφ = KW/KVA

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Find KVA

02/07/2011 6:54 AM

A x V x √3 x 3 / 1000 = KVA

KVA x Pf = KW

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Commentator

Join Date: Oct 2009
Location: Dubai,UAE
Posts: 62
Good Answers: 2
#7

Re: Find KVA

02/07/2011 8:33 AM

KILOWATT (kW) = VOLTS x AMPERES x POWER FACTOR x 1.73
1000

To Convert Between kW and kVA

kW to kVA kW / .85 = SAME VALUE EXPRESSED IN kVA
kVA TO kW kVA * .85 = SAME VALUE EXPRESSED IN kW....

__________________
There are no shortcuts on the road to a great experience.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #7

Re: Find KVA

02/07/2011 12:49 PM

Yes, OK. Do turn off Caps Lock next time, eh?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#9

Re: How to Find KVA

02/08/2011 12:44 AM

For sizing genset,kVA is not enough.You should know the pf of load to find kW of engine. PF varies with current or load. During starting of large motor across the line pf will go down to even 0.3 due to 6times FLA drawn.Voltage/Frequency drop should be within limits at generator terminals as well as motor terminals.

__________________
pnaban
Register to Reply
Participant

Join Date: Feb 2011
Posts: 1
#10

Re: How to Find KVA

02/08/2011 10:41 AM

if you use

440 x [200 x 3phase] x 1.732 /1000

457.248amp

you only know kVA of Load, you don't know kVA of general

Register to Reply
Power-User

Join Date: Jun 2009
Posts: 134
Good Answers: 11
#11

Re: How to Find KVA

02/08/2011 1:19 PM

When using line to line voltage

kVA=ExIx1.732/1000

440x200x1.732/1000=152.4 kVA

Register to Reply