Transformer Bank Loads

02/07/2011 8:36 PM

if the transformer bank(wye delta) has a connected loads of (1 phase and 3 phase buildings ) how i can get the reserve capacity of transformer bank??

the method i made is ,i get the KW rating of all electrical facilities(lights, acu, etc) and i assume a unity power factor,(kw=KVA),,,and add all the KVA off all building loads that connected to the transformer banks.

formula: Reserve Capacity = Transformer bank KVA rating – (KVA off all building loads)

is this possible even the building has a 1phase and 3phase loads????

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Transformer Bank Loads

02/08/2011 11:22 AM

wtf is this question. you may go for Bank Loan instead of bank load.

Register to Reply Score 1 for Off Topic
Anonymous Poster
#2

Re: Transformer Bank Loads

02/10/2011 6:08 AM

calculate for the single phase load seperately and the 3 phase seprately. then sum it up. remember that single phase is without root 3. u are assuming unity power factor, therefore cos tita has no effect. ie all are resistive loads.