A Little Confusion on Surge Arresters

02/08/2011 1:54 AM

Hello People, Kindly help clarify. I am working on the BOQ of a particular HT Transmission line and substations project. One of the specified items is Surge Arrester Earthing. This is a little confusing. The truth is physically I have not really had any involvement with any such equipments. My question is does a Surge Arrester have Earthing cable materials for its connection that are purchased separately or is there an error? Can anyone help me with a picture or something of the connection between the surge arrester and the equipment (HT Cable and/or HT Transformer it is protecting). Please help needed urgently, I'm at a standstill. Thanks in anticipation and Best Regards.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate

Join Date: Dec 2010
Location: Far above all principalities and powers. Nigeria
Posts: 30
Good Answers: 1
#1

Re: A Little Confusion on Surge Arresters

02/08/2011 2:12 AM

You can please explain from this diagram. Are those cables separate items for purchase?

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#2

Re: A Little Confusion on Surge Arresters

02/08/2011 4:10 AM

You have to procure earthing conductor (ECC) and fabricate earth pit, surge arrester supplier will not arrange these for you.

Your picture #1 is a pole mounted transformer and I am seriously doubtful that this would be the case in a T&D substation.

Picture #2 is barely symbolic, instead of fuse you will encounter CB and Isolator, as a standard practice you cannot common transformer and arrestor ground conductors and I expect that in a T&D substation the arrester will be separately mounted on a post / structure instead of transformer frame.

You can check the websites of prominent manufacturers like ABB, SIEMENS, Alsthom GE etc. to see the immages. Just go to www.google.com and make a search for the surge arrester.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply Score 1 for Good Answer
Associate

Join Date: Dec 2010
Location: Far above all principalities and powers. Nigeria
Posts: 30
Good Answers: 1
#3
In reply to #2

Re: A Little Confusion on Surge Arresters

02/08/2011 4:19 AM

Thanks for the info on the earthing conductor, maybe that's what the clients mean by "surge arrester earthing". " You can check the websites of prominent manufacturers like ABB, SIEMENS, Alsthom GE etc. to see the immages. Just go to www.google.com and make a search for the surge arrester." ...I have seen different images from the various sites, but they dont seem to show the wiring connections.

Register to Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#5
In reply to #3

Re: A Little Confusion on Surge Arresters

02/08/2011 5:40 AM

Hire a subcontractor.

Just a minor job like an earth wire run from the motor frame, in the present case you will have to connect the ECC to a terminal at the bottom of surge arrester and will go up to earth pit.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#11
In reply to #2

Re: A Little Confusion on Surge Arresters

08/19/2011 12:08 AM

I have seen separate earths for lightning arrestor,transformer neutral and transformer frame. Verify from your utility.

__________________
pnaban
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: A Little Confusion on Surge Arresters

02/08/2011 4:33 AM

Phone the Surge Arrester manufactuer

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Associate
Engineering Fields - Electrical Engineering - New Member

Join Date: Jun 2010
Location: IEC Domain
Posts: 43
#6

Re: A Little Confusion on Surge Arresters

02/08/2011 9:23 AM

Dear Toba,

Viewing your previous posts including thing one I think our Job Descriptions are alike. .

For Surge Arresters Earthing you would require the following:-

Earth Electrode

Supply and Installation of copper weld earth electrodes, 3 meter long and 3/4'' dia. Driven vertically in ground including the cost of concrete pit all necessary material complete in all respects and conforming to general specification

Earth Test Clamp

Providing, installing earth test clamp made of copper for each down tape. The earth clamp to be installed 5 ft above ground. No connection shall be made to the earth tape below the test clamp
__________________
The Crazy Man Talks and The Smart Man Understands
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7
In reply to #6

Re: A Little Confusion on Surge Arresters

02/09/2011 12:33 AM

How do we know that the lifespan of a surge diverter has expired or damaged?.

__________________
pnaban
Register to Reply
Active Contributor

Join Date: Jun 2008
Posts: 10
#8

Re: A Little Confusion on Surge Arresters

02/09/2011 1:21 AM

I agree with mountk2 that the surge arrester should not be earthed via the transformer tank as this could create serious problems in the transformer in the case of a lightning strike. After all we are trying to protect the transformer.

The earth connection may be made to the substation earthmat as opposed to building a new earth pit.

The cabling will not , normally, be supplied with the surge arrester.

In order to assess the life remaining in the arrester an event recorder can be interposed in the line from the arrester to the earth these units are readily available.

Register to Reply
Member

Join Date: Oct 2010
Location: Egypt
Posts: 7
#9
In reply to #8

Re: A Little Confusion on Surge Arresters

02/09/2011 3:53 AM

I agree with#8 and also I would like to say :

1-You can check also the web site for companies spechialized in earthing systems.

2-In case of considering the number of events as an indication for the arrester life , please note that the surge arresters are usually provided with surge counter and which can help for the number of surges instead of using event recorder with cost pluse to the system price.

__________________
MKHALIL
Register to Reply
Associate

Join Date: Dec 2010
Location: Far above all principalities and powers. Nigeria
Posts: 30
Good Answers: 1
#10

Re: A Little Confusion on Surge Arresters

02/09/2011 5:10 AM

Thanks everyone! I'm really grateful, I understand better now.

Register to Reply
Register to Reply 11 comments