Frame Size and Trippin G Current

02/08/2011 10:31 AM

what is the frame size of a circuit breaker and what is the difference between it and the tripping current AF/AT?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster
#1

Re: Frame Size and Trippin G Current

02/08/2011 11:19 AM

what is the meaning of frame and tripping?? that is the diference,.

Register to Reply Score 1 for Off Topic
2
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Frame Size and Trippin G Current

02/08/2011 2:05 PM

Modern breakers have adjustable or interchangeable trip units, to allow the trip settings to be adjusted to meet the required protective levels.

A "100AT" designates that the circuit breaker should be configured with a 100 Amp trip unit, or perhaps a trip unit that can be set at 100 Amps.

Depending on the details of the breakers you are using, a 100 Amp Trip breaker will require a frame size of 100 Amps minimum. So, you might see 100AF/100AT, or 250AF/100AT, for example.

The frame size is the designation of the maximum continuous current the breaker can carry, and also an indication of its physical size. A 100 AF breaker will be smaller than a 400 AF breaker.

Frame sizes are determined by what the manufacturer offers in their breaker catalog. Typical values for molded case circuit breaker (MCCB) frame sizes are 100, 250, 400, 600, and 800.

Register to Reply Good Answer (Score 2)
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Frame Size and Trippin G Current

02/08/2011 2:13 PM

The search function would have given you access to the dozens of times this has been explained in this forum alone... <sigh>

Frame size is a mechanical spec for a range of breaker sizes, sometimes overlapping. Trip rating is an electrical specification regarding when the breaker will trip, usually on thermal current.

So for example, let's say I need a 125A breaker, which is a short way of saying I want a 125A thermal trip; the thermal current sensor in the breaker will trip at current in any pole that exceeds 125A, the higher the excess the faster it trips (i2t function).

But lets say I have a future need for this to possibly increase to 200A some day. If I bought the 125A breaker as a 125AF / 125AT, when I wanted to change to a 200A breaker, the new breaker will be physically larger than the 125A frame breaker and may not fit. But if I order that 125AT as a 250AF / 125AT, then I'm OK for space in the future.

It's as simple as that.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Anonymous Poster
#4

Re: Frame Size and Trippin G Current

02/23/2011 9:31 PM

How to find Exe MCCb 125AT/225 AF?Do you know what brand or supplier?

Register to Reply
Participant

Join Date: Oct 2010
Posts: 4
#5
In reply to #4

Re: Frame Size and Trippin G Current

03/08/2011 6:50 PM

Tmax generation catalogue will satisfy your need ABB manufacturer

Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

ahmed aboelftooh (1); Anonymous Poster (2); JRaef (1); wareagle (1)