Anonymous Poster

Earthing as Neutral

02/08/2011 2:57 PM

somewhere people use 240V supply one wire & use earth as neutral.then How current is completing its circuit.If earthing resistivity is quite high then,one wire system will work or not.If yes what are the disadvantage of this system.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Earthing as Neutral

02/08/2011 3:15 PM
__________________
The reports of my death are greatly exaggerated.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Earthing as Neutral

02/08/2011 4:51 PM

The disadvantage of this system is that if someone disconnects an earth wire they may receive a fatal electric shock!

Follow British Standard 7671 to avoid unpopularity with the dead victim's relatives, their lawyers and fire insurance companies.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Earthing as Neutral

02/08/2011 5:05 PM

From what I recall our antipodean friends do/did use a single phase earth return system on long rural lines at 6.5KV to earth. But I could be wrong, it's over 10 years since I read about it

England and France use 250KV DC for bulk power transfer using earth as return. I suppose the English Channel with all that brine reduces the ground resistance.

__________________
The reports of my death are greatly exaggerated.
Reply
Participant

Join Date: Feb 2011
Location: Port Pirie, South Australia
Posts: 2
#4

Re: Earthing as Neutral

02/08/2011 10:47 PM

These systems are refered to as Single Wire Earth Return (SWER) and are often used in rural areas where long supply runs are required and the current demand moderate. The supply voltage is in the range of a few tens of kilovolts, enabling the use of high tensile steel conductors (due to the low current) and consequenyly, fewer poles.

The 240v circuit is the secondary winding of a step down transformer and the kv turning of the primary is earthed, as is the 'neutral' of the load circuit. In South Australia the supply voltage is 19kv, sufficient for the return current to make it's way back to the power station. In areas where SWER lines are in use, there can be considerable voltage drop along the ground in the vicinity of the power station due to the earth current.

There have been many fatal accidents involving farm implements contacting SWER lines. LOOK UP and LIVE!

Reply
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#5

Re: Earthing as Neutral

02/09/2011 8:47 AM

I've once saw a well pump with a single wire run along the surface for power..

well?

__________________
High Tolerance is Beautiful
Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6

Re: Earthing as Neutral

02/09/2011 9:11 AM

Australia uses such a system in the outback.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Anonymous Poster
#7
In reply to #6

Re: Earthing as Neutral

02/10/2011 7:20 PM

That's "Injeneur"!