Glass Wall Architecture for High Voltage Indoor Substation

02/09/2011 6:30 AM

Hi

I am from India. We are erecting a indoor sub station for coal handling system of a thermal power plant. in which 11 KV panels are located. We are planning to use glass walls instead of concrete walls for the substation.

My queries are:

1) Is there any technical disadvantages of glass walls instead of Concrete walls?

2) Is there any specifications for glass to be used for such high voltage substation?

3) Is there any standard (specially Indian Standards) Stating that glass walls for 11 KV substation can be (or Can not be) made of glass walls?

In current design distance of panels from wall is 1.5 Mtrs.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Glass wall architecture for High voltage indoor substation

02/09/2011 7:15 AM

Glass walls are probably better insulation than concrete walls.

Glass walls can be seen through.

Other than expense, I don't know of disadvantages.

This sounds pretty neat to me.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2

Re: Glass wall architecture for High voltage indoor substation

02/09/2011 8:01 AM

Don't know about technical. I have seen the damage done by short circuit of gear. Would like to know that the glass would be able to with stand some type of explosion. Or it may send shards of glass out as projectiles if such a mishap should happen. Concrete would be better containment of such a mishap.

You give no info on the type of curtain wall that they wish to use.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#3

Re: Glass Wall Architecture for High Voltage Indoor Substation

02/09/2011 8:59 AM

You may be interested in this. You have to do the free registration to read the whole article, but it looks worthwhile.

http://www.glassfiles.com/library/17/article329.htm

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: Glass Wall Architecture for High Voltage Indoor Substation

02/09/2011 4:55 PM

Toughened glass can be stronger than concrete. So OK go for it, but given the expense, why?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Anonymous Poster
#5

Re: Glass Wall Architecture for High Voltage Indoor Substation

02/10/2011 2:16 AM

hi

Its not usual to a substation to use glass as a wall.it needs ventilation and cables comes inside.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#6

Re: Glass Wall Architecture for High Voltage Indoor Substation

02/10/2011 8:06 AM

Whereas glass does have it eye pleasing qualities in the home or office, the application you ask about seems to be very much over the top for a "run of the mill" sub-station, but if you have the money, why not!

Is this substation going to be a feature within another building with a constant stream of people walking past it, hence the need to use glass as a "make-over"?

If so I would suggest if possible re-locating the sub-station AWAY from pedestrians

You also remembered the thermal qualities of glass. I see you said this substation would be indoors.... any chance of direct sunlight?

As you are in India, where one gets a vast amount of sun, plus temperatures over 50F you might want to think about the "Greenhouse" effect of the glass.

Having work in all over the Middle East & Africa, I do remember large sub-stations having A/C which made it just about tolerable to work in. Now replace the wall with glass... think about the A/C units you would need to keep the sub-station at a temp suitable for workers & equipment if this substation is susceptible to direct sunlight.

Then what about physical expansion of the sub-station or changes to equipment and/or cables, the entry of cables, etc. I know it's usual to have ALL cables fed thru cable ducts underground... but what happens if you need to run cable thru the wall, which I've seen happen may times.

Here's an idea.. re-locate the substation or build your sub-station out of concrete to the required safety specs and wall thickness, THEN front it with glass if its to be a "show case" building on the sides that will be on view. The inside will be a normal temp for worker and equipment, the outside will be a shiny and glass show building.

Everyone wins

__________________
The square root of nothing is what you make it!
Register to Reply
Associate
Netherlands - Member - New Member Canada - Member - New Member

Join Date: Oct 2010
Location: Canada
Posts: 41
Good Answers: 2
#7

Re: Glass Wall Architecture for High Voltage Indoor Substation

02/10/2011 8:39 AM

Which walls are being constructed out of Glass? Just outside walls? then go for it, provided you keep safety of pedestrians in mind that may be passing by the sub station. I f you get a fault in the substation, will the glass be able to contain the explosion, or will it blow the wall out taking innocent by standers with it?

as mentioned before how will you manage cooling, ventilation, cable entry, future modifications, adds and changes?

If the substation is within a larger facility, you may need to provide a fire rating, that cannot be achieved with glass.

What is the benefit of using glass in a coal handling facility? In that environment the glass will be grimy and dusty for most of the time, unless you got a 24/7 window washing crew on standby.

Also, my experience is that when you attempt this type of "first design" you are guaranteed to overlook something, and glass is pretty unforgiving if it comes to modifications after the fact.

As others have said, if you can afford it, go for it. Just think carefully about hte implications.

__________________
I do not feel obliged to believe that the same God who has endowed us with sense, reason, and intellect has intended us to forgo their use. Galileo Galilei
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#8
In reply to #7

Re: Glass Wall Architecture for High Voltage Indoor Substation

02/10/2011 2:09 PM

Re: As others have said, if you can afford it, go for it.

I'd ask who is it that can afford it? Is it taxpayers? Ratepayers (for electricity or something)? Customers? Stockholders? Employees (possibly lower wages or less job security)?

Whoever it is, do they want to pay it? Should they pay it?

Register to Reply Off Topic (Score 3)
Associate
Netherlands - Member - New Member Canada - Member - New Member

Join Date: Oct 2010
Location: Canada
Posts: 41
Good Answers: 2
#9
In reply to #8

Re: Glass Wall Architecture for High Voltage Indoor Substation

02/10/2011 3:42 PM

The points you raise are political in nature. I do not want to seem politically or socially insensitive, but this forum is technical in nature. Who pays for what is not for this forum to answer.

__________________
I do not feel obliged to believe that the same God who has endowed us with sense, reason, and intellect has intended us to forgo their use. Galileo Galilei
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#11
In reply to #9

Re: Glass Wall Architecture for High Voltage Indoor Substation

02/11/2011 2:46 AM

Hear, Hear.. GA from me!! You are VERY correct!

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#10

Re: Glass Wall Architecture for High Voltage Indoor Substation

02/10/2011 5:33 PM

Let's look at it as a glass wall.

We can both see what we're both looking at. But do you see what I'm supposing you think you're seeing.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Off Topic
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#12

Re: Glass Wall Architecture for High Voltage Indoor Substation

02/12/2011 2:52 AM

Apart from all the points already mentioned, you should also consider that since the walls will be of glass, due presence of High Voltage( 11Kv ), static charges may accumulate on the inside glass surface of the substation walls. If it is not properly discarge with suitable device, human may get electric shock when touches by bare hand standing on bare floor due capacitance effects.

__________________
Manindra
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#13
In reply to #12

Re: Glass Wall Architecture for High Voltage Indoor Substation

02/12/2011 11:46 AM

Really? I've never heard of something like that happening (on walls around a substation). Does it happen for concrete walls?

Register to Reply
Guru

Join Date: Aug 2010
Location: Melbourne, Australia
Posts: 740
Good Answers: 24
#14
In reply to #12

Re: Glass Wall Architecture for High Voltage Indoor Substation

07/14/2011 3:10 AM

For that to happen current has to flow, albeit very small current, but glass is an insulator.

Surface contamination could however contribute to such an effect, however that will occur regardless of the wall material....

I see no technical problems with glass walls.

Register to Reply
Register to Reply 14 comments