Circuit Breaker Connector

02/09/2011 3:56 PM

I have 2 110 circuit breakers connected with a small piece of copper wire so they both turn off and on together. I am told this is illegal and the copper wire must be replaced with plastic. What kind of plastic connector is to be used?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Circuit Breakers

02/09/2011 4:06 PM

Depends where you are and what the code says.

Back on the farm, it wouldn't matter.

Register to Reply
2
Guru
Engineering Fields - Electrical Engineering - Analog and Digital Circuit Design Engineering Fields - Electromechanical Engineering - Transformers, Motors & Drives, EM Launchers Engineering Fields - Engineering Physics - Applied Electrical, Optical, and Mechanical

Join Date: Jan 2008
Location: NY
Posts: 1207
Good Answers: 119
#2

Re: Circuit Breakers

02/09/2011 4:12 PM

What make and model breakers?

The breaker manufacturer will usually make a small plastic part to link 2 single-pole breakers so they can be used as 1 double-pole breaker. The manufacturer should specify if this is an approved use of their breakers. Your electric codes will also dictate if this linking of 2 breakers is allowed.

Another choice is to purchase and install a dedicated/approved double-pole breaker. Save the 2 single-pole breakers for any other vacant positions in your panel that might be used for new wiring. If you are not the home-owner and/or are not comfortable changing breakers, find a good licensed electrician to do it for you.

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Circuit Breakers

02/09/2011 4:14 PM

Most manufactures make a clip on bridging handle. Shouldn't cost more than £2-00

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Circuit Breakers

02/09/2011 5:44 PM

"Illegal"? Why? Who is going to prosecute?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Circuit Breakers

02/09/2011 5:58 PM

So one circuit overload pulls both breakers? What is the point of that? Why not leave the other circuit running?

There's something odd going on with the downstream wiring, and it isn't in British Standard 7671, if that's what the word "illegal" is supposed to mean.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#6
In reply to #5

Re: Circuit Breakers

02/09/2011 6:47 PM

Its a north American standard where 240 volt AC is supplied by two 120 volt lines 180 degrees out of phase thus making two breakers necessary on any residential 240 volt circuit.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #6

Re: Circuit Breakers

02/10/2011 5:41 AM

The forum doesn't know that the original poster is on the North Island of the Americas, because it hasn't been stated.

The installation still falls outside British Standard 7671.

OK, so why are the two breakers linked together at all in a two-phase system? Surely the first one to release would disconnect the overload current, so why link them together? One runs the risk of the opening mechanism on one having to operate the opening mechanism on the other irrespective the second one not tripping, which might be the case if the breakers are not identical. If the fault is to earth, then both breakers will operate though not necessarily at exactly the same time.

If isolation is required, then is the time to turn off both breakers.

'Curious' of Dodman's lane.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: Circuit Breaker Connector

02/09/2011 8:46 PM

The clips that the CB mfrs supply are specifically designed to turn off BOTH breakers if one trips. If you use the "bailing wire / duct tape" handyman approach, your rigidity specs may not perform the same function and leave one breaker energized.

So let's take a scenario of a common 240V circuit in a US residence, an electric stove. One of the elements gets old and the connector begins to melt into the metal frame of the stove top. One side of that circuit becomes directly connected as a grounded fault and the short circuit current causes the L1 side breaker to trip. But your little copper wire gizmo does NOT turn off the L2 side because it's too sloppy. The ground fault then has the rest of the heating element in series with the ground connection, so the current is too low to cause an instantaneous trip. It continues pumping current into the ground fault until the breaker trips on thermal current, but by then the kitchen is on fire.

So are the "Electrical Police" going to come out and arrest you? No. But let's say that fire happens and you want to replace your kitchen (assuming the fire did not kill your kids and lose all interest in life). You call your insurance agent, he sends over an adjuster. The adjuster looks at the fire dept report on the cause of the fire, they list this little copper wire set-up and guess what? Your insurance company says "So Sorry, you had an unauthorized use of equipment. You are on your own." So for the cost of a $2.00 little clip, you have sacrificed 10s of thousands of dollars.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Anonymous Poster
#9
In reply to #7

Re: Circuit Breaker Connector

02/09/2011 11:29 PM

So glad that you gave such a good and truthfull answer.

Register to Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#10
In reply to #7

Re: Circuit Breaker Connector

02/09/2011 11:36 PM

This is so funny. I ran across this today with a 240V 2 Pole 5HP Grinder pump.

One of the past "electricians" in this plant did just that with 14 Gage solid wire. Well it tripped off the #7 Breaker, but because it was only 14 Gage wire, #5 Breaker remained on burning out this pump. Now, that said. I do, do this for 2 pole and 3 pole by using 10 Gage solid wire or a roll pin to lock them together. I have never had an issue as the 10 Gage is a perfect fit if I don't have the correct length roll pin. I do also change these out if using the 10 Gage wire to the proper breaker after I order them and only do this in a pinch when making changes to our services. At my location, change is constant... Unfortunately, this pump pumps all the sewage out of the building. They can not replace the pump till tomorrow and the Sh!t is backing up!

Plumber found a plastic plate that jammed the impeller. Had the Circuit breaker tripped both 5 & 7, we would not have had to replace the pump and had the expensive service call, replacement pump expense or backed up Sh!t.

__________________
"Real Bass Players" do not use picks
Register to Reply
Anonymous Poster
#8

Re: Circuit Breaker Connector

02/09/2011 11:25 PM

Any common line conductors need a common trip breaker. The little plastic or metal tye bars do not always work. If you have a Zensco or FPE panel you may want an electrician to install a new breaker, as I have had them blow up on me several times in the 35 years as an electrician. Buy a new breaker and install it. The cost cannot out weigh your life and your biggest investment (your family and property). Hopefully you are not the landload. Good advice on the insurance company too. If you were my nieghbor I would do it for you free. Good Luck my friend.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Dec 2010
Posts: 166
Good Answers: 4
#12
In reply to #8

Re: Circuit Breaker Connector

02/10/2011 7:31 AM

If you have a FPE panel, you may want an electrician install a new PANEL. Those things are notoriously unreliable. There is a reason they don't make 'em anymore.

Register to Reply Score 1 for Good Answer
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: