Anonymous Poster

Energy Level in MCB

02/10/2011 12:14 AM

some of the model MCB's are shown energy level. What is the meaning of energy level,or in the case of MCB?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: energy level in mcb

02/10/2011 3:00 AM

It's, it's ability to break current. On some large CB's it will be 100's KA

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: energy level in mcb

02/10/2011 3:21 AM

Fuses and circuit breakers include these characteristics, among others:

Max or peak short-circuit interrupting capability
Max or peak let-through current
Max or peak let-through energy

These are related, but not 100% correlated with each other (because of time, for one thing). Current is related with magnetic forces that may attract/repel busbars/cables to each other. Energy is related with heating/melting/vaporizing the same.

Bussmann Fuses has good literature on this, and some videos as well.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: energy level in mcb

02/10/2011 4:36 AM

Please stand corrected. It should be Energy Limitation Class. You see, when there is a short circuit, the MCB will trip after certain milliseconds. Won't it? Upto the time the MCB trips for a short circuit, the short circuit current 'I' Amperes will flow for a duration of 't' seconds. There will be I2t energy let through the MCB and the downstream devices connected to this MCB must be capable of withstanding this "let-through" energy from the MCB.

Modern MCBs have a feature called 'current-limitation' wherein due to contact arrangement, there will be repulsive forces between the contacts and it does not require a sensing and signalling from a release to effect tripping of the MCB during a short circuit.

The high repulsive forces generated during the short circuit themselves would cause opening of the contacts. Thereby, current interruption takes place much before the fault current reaches the peak value. This is called current limiting.

When an MCB has the current limiting feature, the let-thro energy from the MCB is reduced and the downstream devices are stressed to a lesser level during a short circuit.

Based on the let-thro energy MCBs are classified under what is known as Energy Limitation Classes.

Hope it is clear.

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #3

Re: energy level in mcb

02/10/2011 4:43 AM

By the by, forgot topost earlier! Aren't you the same "guest" who, of late, has been throwing a series of questions on MCBs? what's the plan? Planning to start an MCB manufacturing unit?

Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5
In reply to #4

Re: energy level in mcb

02/10/2011 2:46 PM

Humm have been wondering????