Delta Connection in IM

02/10/2011 1:39 AM

Hi, My 7.5 kw squirrel cage IM is tripping (taking 5 times rated current even after much time). There is no abnormality in motor and cable. My doubt is on my terminal connection. How should I connect the motor? Either U1-W2, V1-U2, W1-V2 Or U1-V2, V1-W2, W1-U2 (Presently connected in this fashion) Will changing of connection like above makes difference or not??

Register to Reply
Pathfinder Tags: induction motor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Delta connection in IM

02/10/2011 2:44 AM
__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Delta connection in IM

02/10/2011 4:28 AM

It does not matter which way you connect to form the Delta. Only the direction of rotation of the rotor will change between these two connections. I suspect the inertia of the connected load, undervoltage at the motor terminals, harmonics in the power system, etc.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#3

Re: Delta Connection in IM

02/10/2011 8:26 AM

Use a tongle tester to check the current in 3phase after motor is turned ON. Give the motor back for whome you gave for rewinding to reconnect the terminals to star or delta.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Delta Connection in IM

02/10/2011 2:03 PM

10:1 odds says you have a digital ammeter and you have the "Peak" switch left on so it registers the peak and does not drop down again on the meter display.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#5

Re: Delta Connection in IM

02/10/2011 8:15 PM

It looks you have an IEC (new) motor with 6 leads terminal. The motor nameplate should have the detail connection information and you can get it from there. You first need to know the required connection configuration (Star or Delta) for the voltage that you are applying. Then connect as follows:

In case of Delta, U1-W2, V1-U2, W1-V2 and provide the supply to U1, V1, W1

In case of Star, U2-V2-W2 and provide the supply to U1, V1, W1

See this link for more detail

http://hollandindustrial.com/PDF%20Files/European%20and%20American%20Motor%20Connections.pdf

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#6
In reply to #5

Re: Delta Connection in IM

02/10/2011 11:53 PM

Wrong answer in My case. You need to discuss this with the MFG. I have 44 5.5 KW pumps that were "wired by the factory to be wired in WYE for 480V" They sent them wired Delta 480V and never told any one till we burned out 6 of them. Then said, Oh , we re-wired them specifically for you to run in DELTA @ 480V. None of the info on the motor name plate states this, nor does any info accompanying the motors/pumps indicate this. Bottom line, the pumps are wrong anyways and the MFG is replacing all of the 5.5KW to 7.5KW as what was specified in the beginning and these will be WYE configuration. So don't go by what is on the name plate. Test the windings first when dealing with EU motors. Take that extra step. Be safe.

__________________
"Real Bass Players" do not use picks
Register to Reply
Power-User

Join Date: Oct 2007
Location: Canning Vale Western Australia.
Posts: 160
Good Answers: 7
#7
In reply to #6

Re: Delta Connection in IM

02/11/2011 1:37 AM

We are seeing the same thing with smaller motors coming as 415V Y / 240V delta connectionfor the same motor. Many have been connected 415V delta and failed due to high amps.

__________________
I attend work so my dogs can have the good life.
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#11
In reply to #6

Re: Delta Connection in IM

02/11/2011 1:06 PM

This is confusing.

If they were wired to run Delta on 480V, and you supplied 480V to them, then they are OK and can run! Your problem, as it transpires later on in your comment, is that the motors were under-rated and they sent you 7.5 kW motors instead of the 5.5 kW motors that burned.

Register to Reply
Active Contributor

Join Date: Jun 2008
Posts: 15
#9
In reply to #5

Re: Delta Connection in IM

02/11/2011 4:57 AM

@msamad I only want to know that what will happen If I connect it in U1-V2,V1-W2,W1-U2 manner(Delta) ??? Because when the motor shipped at our location, it was connected in that manner.

Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#10
In reply to #9

Re: Delta Connection in IM

02/11/2011 6:17 AM

Nothing will happpen, the motor will just run the same way

Electrical, there is no difference in a connection U1-V2 and V1-W2 and W1-U2

or U1-W2 and V1-U2 and W1-V2.

In both cases you connect the windings in delta.

In both cases the motor will even spin in the same direction if the supply sequence remains the same. Ita est :

  • L1 is connected to U1
  • L2 is connected to V1
  • L3 is connected to W1
Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#8

Re: Delta Connection in IM

02/11/2011 4:47 AM

Please check if your supply voltage matches the motor voltage.

If your motor is 400V delta / 690V Wye

and your supply is 220V it will never work......

Register to Reply
Anonymous Poster
#12

Re: Delta Connection in IM

02/11/2011 2:31 PM

let me know wether the motor is loaded or not if loaded which type of load.

meger the winding of motor

if it was aged or provision of low insulation class you may have this problem

if they provide low insulation class you better go for star connection

Register to Reply Off Topic (Score 3)
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#13

Re: Delta Connection in IM

02/11/2011 8:22 PM

Check the data plate of the motor first,the connection if it is for delta,the voltage given in the data plate for the delta connection must agree with your available source voltage.

For example:3-phase,Δ/Υ,220V/415V.You should connect this motor in delta(Δ),if your 3-phase source voltage is 220Volts.You should connect this motor in star(Υ),if your 3-phase source voltage is 415Volts.

Note that your delta connection should be U1-W2,V1-U2 and W1-V2,while your supply should be L1-U1,L2-V1 and L3-W1.Your star connection should be W2-U2-V2,while your supply should be L1-U1,L2-V1,and L3-W1.

If the data plate states that the motor can be star-delta connected to the line,then you use a star-delta starter for the motor.Ensure that your motor front/end bearings are very free to avoid taking higher currents.

Pls,ensure that your protection devices are given adequate ratings and settings.

__________________
Patrick Whowha
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#14
In reply to #13

Re: Delta Connection in IM

02/12/2011 12:30 PM

"If the data plate states that the motor can be star-delta connected to the line,then you use a star-delta starter for the motor.Ensure that your motor front/end bearings are very free to avoid taking higher currents."

This is not normally stated like that. If the motor is rated in Δ for 415 V and there are 6 wires coming out, then you can use it with a star-delta in a 3 phase supply with Line-Line volts = 415 V.

Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#15

Re: Delta Connection in IM

02/16/2011 5:14 AM

Please check the polarity of the motor coils by approved method.Then make connections as already stated(Star or Delta). Ensure that the motor rating is correctly selected in respect of Kw capacity,Torque requirement, GD^2 value of the load(driven equipment)&GD^2 value of the motor and correct selection of the voltage rating, starter connections. Then only switch ON the power supply.

__________________
Manindra
Register to Reply Score 1 for Off Topic
Register to Reply 15 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); anvesh (1); Doggoneit (1); electricalexpert65 (1); Jimh77 (1); JRaef (1); LAA_Lucke (2); manindra (1); msamad (1); Patrick Whowha (1); rudy.leurs (2); TonyS (1)