4-20 mA For 500 Meter Distance

02/13/2011 11:32 AM

Dear All,

We have 3 loops in our existing mill with distances of 500 meters from transmitters to marshalling cabinets of DCS carrying 4-20 mA. We have now modification project, can we use the same distance or we should have some remote I/Os in the field.

Best Regards,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: 4-20 mA for 500 meter distance

02/13/2011 11:44 AM

What have you modified? Has the distance changed? Is 500m the new distance, or the old? Was it previously working?

Need more information. You are not helping yourself by posting incomplete data.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: 4-20 mA For 500 Meter Distance

02/13/2011 1:17 PM

500m is as nothing to a properly-installed 4-20mA current loop. If loop resistance is perceived to be a problem at that distance, the usual remedy is to increase the power supply voltage.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Mar 2010
Posts: 50
#3

Re: 4-20 mA For 500 Meter Distance

02/13/2011 10:54 PM

Dear JohnDG,

We are working in paper mill. Firstly it was 2 layer machine but now it is going to be three layer machine. For third layer we have modification project with 1150 more I/Os.As discussed with you, some of the I/Os have distance more than 500 metre from DCS. We have to decide whether we can use the same scenario or remote I/Os can be used.

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#5
In reply to #3

Re: 4-20 mA For 500 Meter Distance

02/14/2011 3:38 AM

Shouldn't be a problem, provided (as has been said) the power supply voltage is high enough to drive 20mA through the loop.

Makes me wonder, tho', if this isn't a bit of a retrograde step. Why have a Distributed Control System, and still run hundreds of cables back to a central location?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#6
In reply to #3

Re: 4-20 mA For 500 Meter Distance

02/14/2011 5:04 AM

How many I/O's are about 500 m away from the central unit out of the 1150 I/O's?

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#10
In reply to #3

Re: 4-20 mA For 500 Meter Distance

02/15/2011 5:17 AM

If there will be about >50 I/O 500 meters away, in my personal opinion, having it organized by a remote I/O is preferably best. You don't need your system to get complicated with wiring and conduits just like varicose veins , further, it will be inconvenient for maintenance technician to trouble shoot a system (when malfunction) having a distance considerable enough to be tiring from walking back & forth.

Having a remote I/O will let you do the troubleshooting job isolated and convenient.

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply
Anonymous Poster
#4

Re: 4-20 mA For 500 Meter Distance

02/14/2011 2:36 AM

Depends on the cable specification. Check the voltage drop calculation for 500m with cable specification, calculated voltage shall not be bellow than instrument required minimum voltage.

Register to Reply
Power-User

Join Date: Dec 2010
Location: Tulsa, OK
Posts: 184
Good Answers: 2
#7

Re: 4-20 mA For 500 Meter Distance

02/14/2011 7:43 AM

As indicated by others if you up the voltage feed and make the cable big enough you might get good signals back.

If you want you could use an I/O with a fiber optic link and then it will work also.

The issue here is not really the distance rather the cost of so many cables coming and going, which tend to be expensive.

Register to Reply
Active Contributor

Join Date: May 2008
Location: Mumbai
Posts: 11
Good Answers: 1
#8

Re: 4-20 mA For 500 Meter Distance

02/14/2011 8:27 AM

We have connected transmitter at around 1.2 km from DCS with 24VDC power supply and there was no issues at 20mA also. A transmitter requires around 12-15 volts for proper working and there wont be any potential drop across barrier. So 500mtrs won't be a problem and try to connect a sample transmitter at that distance to decide yourself

__________________
Nikunj Jain
Register to Reply
Associate

Join Date: Jun 2008
Location: Houston
Posts: 30
#9

Re: 4-20 mA For 500 Meter Distance

02/14/2011 10:22 AM

The real challenge is not whether the 4-20 can transmit over that distance also care can be taken to see that the voltage drop does not cause a problem through proper wire size selection, but the installation cost of wiring many devices even in home run cabling efforts can be lowered by using remote IO... Many systems now offer Ethernet versions that allow faster transmission paths and if they support fiber then noise issues are also reduced to only the areas where the transitions take place. The justification has to consider the area classification for the remote IO and if it can be placed centrally in the IO to minimize wiring runs this can save installation time and startup time if engineered properly... The breakpoint on remote IO can be as low as 60 IO depending on area classification and utilizing the best method of protection for the installation such as intrinsic safety methods over explosionproof for division 1 areas...

Register to Reply
Participant

Join Date: Feb 2011
Location: Indonesia
Posts: 3
#11

Re: 4-20 mA For 500 Meter Distance

02/18/2011 10:44 AM

If you have only three loops with distances of 500mtr from your control room, then you don't need to put any remote I/O. If the I/O becomes more than 50, you need to install a remote I/O panel to avoid the cost and cabling only.

__________________
P. Paul
Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#12

Re: 4-20 mA For 500 Meter Distance

02/21/2011 12:24 AM

My Experienced, I've installed for annunciator distance 720m with regular control cable 2,5 mm shielded one tray with other DC cables. It has bad measurement, some like intermittent, first we suspect the gauge is damaged. We changed but still problem. So we change special for instrument cable, its very expensive !...and done, all signal never get traffic jam..means since that every thing its OK

__________________
One system
Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

AA (1); Anonymous Poster (1); JohnDG (2); loadshare (1); nikunjjain (1); Noudge79 (2); p_prabir (1); PWSlack (1); ral412 (1); vargaalex (1)