Isolating Disturbing Loads

02/14/2011 5:53 AM

Hi, I think isolating the disturbing load is a bit confusing to me, if a load is disturbing namely it starts up with a big current such as motors welders etc. so what difference makes to isolate these loads from the sensitive ones .İn essence they really are fed through the say same transformer isnt it right ? What do you advice when this issue is up to be discussed?

__________________
jinxnao
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Isolating Disturbing Loads

02/14/2011 10:07 AM

Source Voltage drop cannot be minimised if they are fed from the same source. But, at least the bus voltage drop can be minmised, if they are fed from different busses. Moreover, the impedance between the two busses will reduce the interference from the non-sensitive loads affecting the sensitive loads.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Isolating Disturbing Loads

02/14/2011 12:33 PM

Both the disturbing load and the sensitive load are ultimately powered from the same source. However, unless your power source is directly connecting to these devices at the local distribution voltage (like a portable generator) then all of the grid transformers are doing a very subtle thing that most people do not grasp. On every cycle of your power fluctuation the magnetic core of each transformer can only store and deliver a fixed maximum amount of energy. The grid upstream of this transformer can provide much more energy so the voltage sag upstream of the briefly overdriven transformer is minimal. By having the sensitive load connected to a transformer that is not overdriven (isolated) the sensitive load gets power with little to no fluctuation.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#3

Re: Isolating Disturbing Loads

02/14/2011 10:26 PM

Connect the disturbing load to its own distribution transformer. The disturbance will not be eliminated - but greatly reduced.

Register to Reply
2
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#4

Re: Isolating Disturbing Loads

02/15/2011 7:11 AM
  1. Suppose your supply is through, say, 300 kVA transformer.
  2. That is 100 kVA/phase at 230V, which is 100/0.23 amps/phase = 435 amps.
  3. The rated load would be 230/435 ohms = 0.53 ohms.
  4. A typical impedance for such a transformer would be 3.75%, which makes 0.0375 x 0.53 ohms = 20 milliohms say.
  5. If you feed your welder from a 30 amp circuit with the maximum 4% cable voltage drop, its source resistance will be (ignoring transfo) 0.04 x 230/30 = 0.3 ohms.
  6. So if you connect a sensitive load at the same place as the welder, the common resistance is 0.3 ohms, a 30 amp welder current on/off will cause 9 volts change [30 x 0.3].
  7. However, back at the transfo 30 amps x 20 milliohms is only 600 millivolts
  8. So if you connect the sensitive load to the transformer through its own cable, it will see only 0.6 volt variation due to the welder, instead of 9 volts.
  9. In practice, it would not be good to run the welder supply cable and the "sensitive" cable together, because induction and capacitance will couple high frequency noise from one cable to another.
  10. A good separation e.g. 150 mm is vastly better than touching! This needs a deliberate policy of feeding sensitive loads from their own circuit spaced away from other circuits.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#5

Re: Isolating Disturbing Loads

02/15/2011 1:33 PM

Adding to post #4. An important effect is distance.

  1. Suppose welder and sensitive equipment [SE] are both 20m from the power origin. Each is connected by separate cable,kept apart as suggested in post #4.
  2. The cable run between welder and SE is 40m.
  3. It is generally found that interfering switching devices are within 10m of the affected equipment, so 40m separation is good.
  4. If the SE is powered from the same cable as the welder, there may be just a few metres of cable between the two.
  5. N.B. ordinary power wiring has enough attenuation at high frequency to suppress the really sharp "spike" edges which affect digital equipment within the 10m mentioned. The PVC insulation commonly used has high loss at high frequency compared to e.g. polyethylene, used for high frequency signal cables.
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#6
In reply to #5

Re: Isolating Disturbing Loads

02/18/2011 8:02 AM

If the SE is powered from the same cable as the welder, there may be just a few metres of cable between the two. what do you mean with this?

__________________
jinxnao
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#7
In reply to #6

Re: Isolating Disturbing Loads

02/18/2011 9:05 AM
  1. Suppose welder and SE are both plugged into sockets of one supply circuit.
  2. Welder and SE will include, typically, 1.5 m of cable each (to its plug).
  3. That is 2 x 1.5 = 3 metres cable, which interference must pass through between welder and SE. There could also be cable between sockets.
  4. For small numbers, one can say "few", especially when the number is not known or variable or is much less than usual.
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#8
In reply to #7

Re: Isolating Disturbing Loads

02/18/2011 9:31 AM

Thank you for your explanations. But I wonder what is the golden rule of this interference situ. Is there any rule you can cite?

__________________
jinxnao
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#9
In reply to #8

Re: Isolating Disturbing Loads

02/18/2011 12:23 PM

One rule! Difficult!

  1. Some interference problems will not be solved until you have done everything the right way - leaving out just one "best practice" measure or restoring one thing "as was" leaves the problem in "full health". But they are usually the cases where no-one thought about interference in making or installing.
  2. The best Project Manager for whom I worked [his contracts made money - even when it looked like a loss when he was handed it] said often "Doing work on-site costs ten times as much as in the factory and fixing design problems costs even more". He was very supportive when a problem was identified. And very stubborn when what customers wanted had been identified in our tender as "not provided" but was in the customer's specification and unusual. I particularly remember a customer who wanted all control panels to be made of 3 mm minimum thickness steel - he got them - at extra cost!
  3. In the same way, fixing an interference problem - finding out what it is and then curing it - is far more expensive once equipment is in operation than during the design and manufacture. If something is new to you, it is better to bear the cost of investigation and tests than have to fix them in operation with an unhappy customer.
  4. If there is a rule it is "Always think IF an equipment you want to use is likely to be susceptible to interference or be a generator of interference - and specify some installation and equipment standards when there could be a problem".
  5. Ask suppliers what EMC (ElectroMagnetic Compatibility - emissions and susceptibility) standards with which their equipment conforms. AND what EMC tests they have have done. Ask to see their test results! It is possible to declare conformity without doing tests! I well remember a foreign company which got a sub-contract for a governor on their low price. It turned out they had only done radiated susceptibility radio frequency tests, with the equipment in an "RF proof" cabinet and all the cabling under the metal floor of the test room. Since they were required to meet military standards, which include susceptibility and emissions at the cables and with radiated fields their submission was an example of what my first boss called "weasel wording". Meaning words carefully chosen and intended to "worm" out of a potential contractual obligation, like the long, thin agile predator called a weasel!
  6. The European EMC standards are strict. I suggest you look at them. But they assume you use good practice for use of segregation of cabling and shielded cable/housings, when needed, as specified by the maker. But there is a "loophole" for the "weasels" in the susceptibillty criteria - it is up to the maker to specify what constitutes an acceptable performance during test, so if it were a meter they could have specified 10% error even though the brochure says 1%!
  7. Note, the RF field strength specified for heavy industrial equipment to EN generic standards is 10V/m - but military goes up to 200 V/m on the outside of ships and aircraft. Motor industry RF standards [with so much electronics used] are now very good - if you park a car on a public road next to an airport 200 V/m is possible.
Register to Reply Score 1 for Good Answer
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (4); electricalexpert65 (1); jinxnao (2); olehwi (1); redfred (1)