Main and Transfer Switchyard

02/14/2011 6:31 AM

In main and transfer switchyard any one circuit breaker fails how to connect the bus coupler bay

help me

__________________
Helping Hands Are Greater Than The Praying Lips
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: main and transfer switchyard

02/14/2011 7:11 AM
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Main and Transfer Switchyard

02/14/2011 3:17 PM

Quote

"In main and transfer switchyard any one circuit breaker fails how to connect the bus coupler bay

help me"

Have you the slightest idea of what you're doing. No one in their right mind would let you loose in a switchyard.

I'm sorry if this sounds offensive but you did say "help me".

I'm trying to keep you alive!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#3

Re: Main and Transfer Switchyard

02/14/2011 10:37 PM

hello engineer,

better you keep off from the switchyard. anyway, when main CB fails, that line load will be shifted to the transfer bus through transfer bus isolator and the line will be connected to the main bus by closing the transfer bus coupler CB. Now all the trips issued by the line protection relays will be delivered to TBC CB and not to the faulty line CB. One disadvantage in this scheme is at a time, only one breaker can be put into transfer. so this is mostly used in 110, 132, 220kV grids stations.

__________________
You don't understand anything until you learn it more than one way.