What should be the current setting & time setting in the Current Unbalance Element in a Motor Protection Relay? My setting range is:
Pick-up Current setting: 0.1 to 0.8 Im
Time Setting: 1 to 8 seconds (when I2 = I1)
The element follows an IDMT Charectersitics.
Re: Current Unbalance Protection Time Setting
02/15/2011 10:27 PM
It will depend on your application.
if you have a balanced load i.e. pump then you can look for small differences with a quick time pick up.
if you have an unbalanced load i.e. crusher, then i suggest you look at the manufacturers data and find what the expected unbalance is so you can set the protection to operate outside of the bandwidth thus avoiding any nuisance trips but protecting the equipment before damage is done.
you also need to make sure you protection is discriminated with upstream current unbalance protection ...if there is any.
02/15/2011 10:28 PM
you can go 0.15 Im with time as 1 TMS. Bcoz in practical, there will be always some % I2/I1. i think wat you mentioned in the "Time" is TMS since you have said the element is IDMT Charectersitics
You don't understand anything until you learn it more than one way.
Good Answers: 170
02/16/2011 12:42 AM
Thanks! But, can you trace it back to some Standards as to the withstand capacity of motors for current unbalance?