Current Unbalance Protection Time Setting

02/15/2011 12:28 PM

What should be the current setting & time setting in the Current Unbalance Element in a Motor Protection Relay? My setting range is:

Pick-up Current setting: 0.1 to 0.8 Im

Time Setting: 1 to 8 seconds (when I2 = I1)

The element follows an IDMT Charectersitics.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Member

Join Date: Feb 2010
Posts: 9
#1

Re: Current Unbalance Protection Time Setting

02/15/2011 10:27 PM

It will depend on your application.

if you have a balanced load i.e. pump then you can look for small differences with a quick time pick up.

if you have an unbalanced load i.e. crusher, then i suggest you look at the manufacturers data and find what the expected unbalance is so you can set the protection to operate outside of the bandwidth thus avoiding any nuisance trips but protecting the equipment before damage is done.

you also need to make sure you protection is discriminated with upstream current unbalance protection ...if there is any.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#2

Re: Current Unbalance Protection Time Setting

02/15/2011 10:28 PM

you can go 0.15 Im with time as 1 TMS. Bcoz in practical, there will be always some % I2/I1. i think wat you mentioned in the "Time" is TMS since you have said the element is IDMT Charectersitics

__________________
You don't understand anything until you learn it more than one way.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #2

Re: Current Unbalance Protection Time Setting

02/16/2011 12:42 AM

Thanks! But, can you trace it back to some Standards as to the withstand capacity of motors for current unbalance?

Register to Reply
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); ellisamatt (1); vijaymail_electrical (1)

Previous in Forum: How to save 275kV Transformer with Furan content exceeding 4500ppb   Next in Forum: Alternatives to Hipot Testing

Advertisement