Hydrotest of Vessels

02/16/2011 2:35 AM

I want to know the code reference and procedure as to what pressure to use for hydrotest when piping is welded with the nozzle of the vessel?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Hydrotest of Vessels

02/16/2011 3:06 AM

Most (but not all) vessel codes require vessels to be hydrostatically tested at 1.5 x MAWP (maximum allowable working pressure). Various other piping codes may require a different test pressure. If higher, this may require that pressure vassels and relief valve be isolated from the piping when performing the pipe test. For example, in most of the U.S., ammonia refrigeration high-side vessels are designed for 250 psig, but high-side piping must be nitrogen-tested at 300 psig. (At least it used to be that way, but this may since have been updated.)

This whole business depends on local code requirements.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.