Anonymous Poster

Differential CT

02/16/2011 10:36 PM

What will happen if I use 5P20 protection class CT for differential protectionn? whether it will works?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#1

Re: Differential CT

02/17/2011 12:07 AM

It will work till you get a fault. Bcoz, 5P20 class have lower kneepoint voltage than PS class and so, it will get saturated soon for higher fault currents. So it will be giving nuisance trippings for external faults too. PS class have higher saturation point and your protection will be stable even for external faults which draw large currents. So its preferable to use only PS class cores for special protection for better stability and sensitivity.

-Vijay

__________________
You don't understand anything until you learn it more than one way.
Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#2
In reply to #1

Re: Differential CT

02/17/2011 7:17 AM

Multifunction Numerical Relays beeing used these days receive CT secondary input from a CT core having 5P20 class to provide all types of relevant protections including differential protection. According to Relay manufacturers this is OK.What are your comments/observations ?

__________________
Learning is a never-ending process.
Reply
4
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #2

Re: Differential CT

02/17/2011 8:31 AM

I beg to differ. a 5P Class CT's composite error is + / - 5%. That means a + 5% CT also will be labelled as 5P and a - 5% CT too. If for the differential protection, these CTs are used, it may so happen that the Primary Side CT is 5P with +5% error and the Secondary Side CT is also 5P, but with a -5% error. Under such a condition, if the relay bias setting is 10% or less, even during normal operations, there can be 10% differential current and the relay would operate. This is not preferable. So, one has to go for only PS Class CTs for differential.

Reply Good Answer (Score 4)
Reply to Forum Thread 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); spradhan (1); vijaymail_electrical (1)

Previous in Forum: Information needed   Next in Forum: Clearance from Transformer Oil Containment Pit to Fence

Advertisement