Clearance from Transformer Oil Containment Pit to Fence

02/17/2011 12:36 AM

Please help me wih code clearance requirements for an oil filled padmount transformer loacted near a substation fence. CSA and OSHA requirements in particular. Code references? I checked the CSA code the minimum distance should be 6m from transformer to any wall or window of building. I f this distance not achievable then install fire wall. But whats about substation fence when transformer live part is 4.5 m far from fence and oil pit 2 m from fence

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: Clearance from Transformer Oil Containment Pit to Fence

02/17/2011 1:45 PM

In the US, you should look at the National Electrical Safety Code (NESC) for clearances from exposed live (energized) parts such as the transformer bushings and connecting conductors to grounded facilities such as fence. That minimum clearance depends on voltage. You did say that it is a padmount, so I'm not sure that this would apply.

Clearances for the oil containment do not depend on this. Design of the containment needs to take into account 2 main things: maximum "footprint" of the transformer, so that any leaks dripping off end up in the containment, and and maximum volume of oil required to be contained. The oil containment is not energized (usually concrete), so you don't need to deal with it in clearances unless there is something external that is grounded (railing or other metallic structure). Then you apply the NESC just as if it were a fence or other such.

I believe there are other IEEE standards that give requirements for clearance from a transformer to a building or other structure that you have to protect in the case of fire, but I don't know which standard # it is (there are so many).

__________________
To get the right answers, first you need to ask the right questions.
Reply
Guru

Join Date: Dec 2007
Location: California
Posts: 2363
Good Answers: 63
#2
In reply to #1

Re: Clearance from Transformer Oil Containment Pit to Fence

02/18/2011 12:34 PM

Hmm, so it sounds like from the statement above, that technically you could put the security fencing inside the oil containment pit if the pit was wide enough for adequate clearance from the energized systems. Usually in other systems we are required by the standards of practice to maintain security fencing at least a distance further than a person might be able to reach through the fence, but there are other issues to consider also, safe ingress/egress and mobility within the fenceline for o&m. Generally, it is offset 2 to 3 feet, around the perimeter is good. Allows movement around the facility and separation from potential outside access.