HOW TO CALCULATE GENERATOR LOAD IN AN APARTMENT.

LOAD FOR BLOCK1=194650VA

LOAD FOR BLOCK 2=79190VA

EQUIPMENT LOAD=32587.5 VA

WHAT HP WATER PUMP SHOULD BE USED IN AN THREE STOREYED APARTMENT?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: ELECTRICAL DESIGN

02/17/2011 11:14 AM

What do you want to know? Generator or pump rating? Your question makes no sense!

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Electrical Design

02/17/2011 4:04 PM
  1. Turn off Caps Lock. Readers of this forum are case-sensitive.
  2. Add the three figures together. Assuming these loads are on all the time would give the maximum generator capacity for sizing purposes. If they are not on all the time then downsize the generator by the diversity factor of the load.
  3. The shaft power required by any incompressible fluid mover is the same as it has always been - the volumetric flowrate multiplied by the pressure rise divided by the efficiency.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#3

Re: Electrical Design

02/18/2011 5:15 AM

Dear Guest, Add up all the loads.Use a diversity factor of 0.7 & a load factor of 1.25 ( to take care of the starting loads of the equipments) DG Kva= 306.427 x (0.7 x 1.25)= 268.123 Kva. Select the DG set nearest to 268 Kva. Choose 250 or 320 Kva depending upon the per Kva cost of the set & operational and Maintenance costs. Manroop.Chennai.