ABB 15 HKS Breaker Fault

03/01/2011 3:37 PM

Hi in the ABB switchgear breaker type 15-HKS (15kv breaker), when racked in tried to close the breaker immediately opened. Put another similar breaker in the cell and closed the breaker it holds fine. Sure the breaker has problem, could you suggest what would be a highly possible scenario.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#1

Re: ABB 15 HKS breaker fault

03/01/2011 4:40 PM

It's been a while since I worked one of these but off the top of my head two items that come to mind are:

Is the rack in/out mechanism fully engaging when clamped in? If my memory serves me, there should be two to four limit switches that close when racking in, check these.

Is the trip button (if equipped) sticking and/or wiring OK?

I tried to Google "ABB breaker type 15-HKS trouble shooting" and a few variations and did not come up with much.

Have you tried contacting ABB tech support?

__________________
The first 5 days after a weekend are always the hardest................................
Reply Good Answer (Score 2)
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#2
In reply to #1

Re: ABB 15 HKS breaker fault

03/01/2011 4:59 PM

"there should be two to four limit switches that close when racking in,"

Sorry - should have been "when racked in"

__________________
The first 5 days after a weekend are always the hardest................................
Reply Score 1 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: ABB 15 HKS Breaker Fault

03/01/2011 6:19 PM

Check the isolation mechanism, I've had the same problem myself.

__________________
The reports of my death are greatly exaggerated.
Reply
Anonymous Poster
#4

Re: ABB 15 HKS Breaker Fault

03/01/2011 10:57 PM

Please note;

Whatever you do please do in proper isoaltion , and don't force the breaker to go in. There must be some problem in the reacking mechanism or else where and consequences are dangerous.

Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#5

Re: ABB 15 HKS Breaker Fault

03/02/2011 4:05 PM

The breaker is not properly reset,remove or rack out,check spring and be sure its in good position,adjust properly if not in good position,reset again,rack in and close breaker.

I have experienced similar problem and made several trials to reset and i succeeded to close the breaker.

__________________
Patrick Whowha
Reply
Reply to Forum Thread 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); KJK/USA (2); Patrick Whowha (1); TonyS (1)

Previous in Forum: icbc@windowslive.com   Next in Forum: How Do I Decide My Power/Current/Voltage Input

Advertisement