Earth Fault And Earth Leakage

03/05/2011 2:31 AM

Dear all,

I am getting stuck with these two kinds of protection. The first one is earth fault protection which is using 3 CTs for three phases and 1 for the neutral wire. The protection principle is based on the unbalalce current on these three phases. The other one is earth leakage current protection. My question fot this is what are the differences of these two protection?

Moreover, how many percent of unbalance current would be acceptable in the power system?

Regards,

__________________
Anything that can go wrong, will go wrong
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Earth Fault And Earth Leakage

03/05/2011 10:55 AM

Earth fault is the unintentional (or sometimes accidental) connecetion of phase conductor with earth; generally the magnitude is high (of the order of a few tens or hubdreds or even thousands of Amperes).

Earth leakage is leakage current flowing to earth from the phases thro the insulation; generally the magnitude is very low (of the order of milli Amperes).

Please remember, there could be eath leakage currents in a perfectly healthy & unctional circuits too, thanks to filters.

Now, to the second question, the answer depends upon whether you have rotating electric machinery connected to this supply. If yes, then 5% Voltage Unbalance (corresponding to about 30% current unblance is maximum permissible). If rotating electric machiney is not present in the system, then talk to the transformer manufcturer as to the acceptable level of unbalance in his transformer.

Register to Reply Good Answer (Score 2)
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#2
In reply to #1

Re: Earth Fault And Earth Leakage

03/05/2011 11:29 AM

electricalexpert65:

Thank you for your reply, after installation, the earth fault protection relay is tripped. The calculation showed me that the unblance current protection is set at 30%. Does it mean that the power system has accidental connection with earth? Or the relay tripped because of unbalance currents only?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #2

Re: Earth Fault And Earth Leakage

03/05/2011 8:48 PM

It could be either. If you don't want your earth fault relay to trip for unbalance currents, provide a CT in the neutral and connecet it residually to the phase CTs. Then the earth fault relay would trip only for genuine earth faults.

Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#4
In reply to #3

Re: Earth Fault And Earth Leakage

03/05/2011 9:11 PM

electricalexpert65:

Still not so clear with what you mean. I have 4 CTs installed to 3 phase and 1 neutral already.

What you mean by "provide a CT in the neutral and connecet it residually to the phase CTs".

The relay manual says that the percent of ILn "earth fault current" shall be from 120% to 200%. What does it mean by that? Does it mean the unbalance current? If not, why it provides us such a big limit of 200%?

Regards,

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5
In reply to #4

Re: Earth Fault And Earth Leakage

03/05/2011 11:03 PM

What is the relay (make & model) you are using? And, what is the earth fault element setting?

If you already have provided 4 CTs and still the e/f element is tripping, then it could indicate a genuine earth fault.

But, wait, you had said that this element trips on switching ON. Then, probably you must be using a Numerical Relay, where the earth fault current is sensed by sensing the zero sequence component of the phase currents. And, during switching ON of reactive loads, there could be great unbalance in the phase currents, due to inrush currents, and, the zero sequence current will be more than the setting made.

The solution is to introduce a time delay of about 100 milli seconds in the erth fault element, by which time the inrush would have subsided. Or you can de-senstise the e/f element by providing a stabilising resistor.

With more details about the relay and settings, I can comment further.

Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#6
In reply to #5

Re: Earth Fault And Earth Leakage

03/05/2011 11:29 PM

electricalexpert65:

It is a Mikro relay and a combination of overcurrent (OC) and earth fault (EF) protection. We have set it as 30% of the maximum current on the total loads.

Yeah, it is correct, as I have stated. But, several days later after this question was posted on here. We got the other EF tripping of the breaker. We thought that the the current was too low and we added up with the fire pump capacity (capacity up to 95kW). So, now, the setting current is 30% of the total load plus the fire pump. It was around 150Amp. The total current is around 570Amp.

However, the breaker tripped again and we one more time increased the setting up to 50% of the total load. Will update if there is anything new.

By the time setting, we have set is at 5 seconds to increase the endurance.

Special note: I have recorded the three phases and seen that the worst unbalance case was just around 10%. The average unbalance during 4 hours or recording was 8.1%. This cannot explain if we say the breaker was tripped by unbalance current because the setting is at 30%.

What you mean by adding up with stabling resistor?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Active Contributor

Join Date: Aug 2010
Posts: 22
#7
In reply to #6

Re: Earth Fault And Earth Leakage

03/06/2011 9:05 PM

I am wondering about your question. Fist of all please note that the difference between those relay: 1. Unbalance Protection (66 as per ansi relay code) 2. Earth fail protection (51N, 50N..) 3. Earth leakage protection If you are talking about Unbalance protection (nomaly for motor protection) then 30% setting for unbalance current is ok, and your relay tripping is not cause by unbalance current. and i agree with electricalexpert the reason maybe due to the inrush current. if so farther study need to be considered.

Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#8
In reply to #7

Re: Earth Fault And Earth Leakage

03/06/2011 10:31 PM

nguyenkhoadung98:

If it was not tripped by unbalance current, we have inscreased the total current as large as 578A then set the EF current at 30% (which means 173A).

The breaker still tripped by EF.

Base on those facts, is there any possbility that our power system has contacted to earth in some area? Can we eliminate the possibility of unbalance current?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Active Contributor

Join Date: Aug 2010
Posts: 22
#9
In reply to #8

Re: Earth Fault And Earth Leakage

03/06/2011 10:59 PM

We are clear that your relay donot trip by unbalance current, so no need to care about unbalance current. The matter cause by other function (earth fail for exam.). we need many information to check your earth fail setting is correct or not. 1. Short circuit study report 2. System information like: location of your relay, transformer vector group,.... ...... with those information you gave, i have no idear for relay setting, excluding unbalance setting.

Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#10
In reply to #9

Re: Earth Fault And Earth Leakage

03/06/2011 11:28 PM

The location of the relay is after the transformer.

But I have the other question right here since you mentioned about the Vector group. Is there any affection to the EF relay function if we change the phase sequence.

Lets say from transformer outgoing: (L1,L2,L3) and to the beaker incoming: (L2,L3,L1)...

__________________
Anything that can go wrong, will go wrong
Register to Reply
Active Contributor

Join Date: Aug 2010
Posts: 22
#12
In reply to #10

Re: Earth Fault And Earth Leakage

03/07/2011 12:45 AM

If your CT (current transformer) is correctly installation (phase sequence as per transformer outgoing)=> no problem. If your CT install according to CB outgoing => no problem for 50, 51, 50N, 51N, and other overcurrent relay, but for differential relay (87, 64R...) very big problem

Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#14
In reply to #5

Re: Earth Fault And Earth Leakage

03/11/2011 12:20 PM

electricalexpert65:

Still dont understand what you want to imply from this:

"And, during switching ON of reactive loads, there could be great unbalance in the phase currents, due to inrush currents, and, the zero sequence current will be more than the setting made".

Are you really electrical expert?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#15
In reply to #14

Re: Earth Fault And Earth Leakage

03/13/2011 9:59 AM

I am very much tempted to reciprocate your "mud-slinging"; but, this forum and my maturity has taught me to be calm. I don't need to prove my expertise to anybody.

Now, to answer your question, please refer to the Areva NPAG. It is mentioned in this guide book - in the chapter on Motor Earth fault protction - that what I had said can very much happen. If you are still not staisfied, then please attend to our 4-days training programme on protective relaying. You can, then understand, first-hand, whether I am an electrical expert or not.

By the by, politeness is a virtue.

Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#16
In reply to #15

Re: Earth Fault And Earth Leakage

03/15/2011 12:00 PM

I appologize if my words hurted you. I hope there would not any misunderstanding between us. I repect you and the other gurus by what you have been contributing to the forum.

You know, not only knowledge and experience. What I have learnt from this forum is the positive attitude like what you did in the previous post. To me, it is great. That is the first virtue for ones who want to become a professional engineer.

From this, we see that CR4 is a truthful place of engineers for discussion.

Thank you,

__________________
Anything that can go wrong, will go wrong
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#11

Re: Earth Fault And Earth Leakage

03/06/2011 11:58 PM

This protection relay gimme NUT !

__________________
One system
Register to Reply Score 1 for Off Topic
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#13
In reply to #11

Re: Earth Fault And Earth Leakage

03/07/2011 12:55 AM

I think that the problem is much clearer at the moment. All I need to do is to find if it is really a case of earth fault where the phase is connecting to earth.

This is an improvement project and sometimes the people in this factory uses the earth wire as a neutral wire. This is I have just known.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

electricalexpert65 (4); hien.nguyenquoc (8); loadshare (1); nguyenkhoadung98 (3)

Previous in Forum: Project Topic   Next in Forum: Design Control And Power Circuits

Advertisement