Motor Wdg. Start And End Lead Identification.

03/05/2011 6:25 AM

there r 6 nos. wdg. leads coming out of motor without any identification. i want to identify start and end lead of each wdg. for connection. is there any test to identify start and end lead of each wdg. of motor without open motor.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#1

Re: Motor wdg. start and end lead identification.

03/05/2011 6:39 AM

Can you describe the motor?

Like;

how big is it?

or anything written on it?

or what it came out of?

or where you found it?

Can you post a picture of it?

Any of the above may get the possibilities down below 10,000

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply Score 1 for Good Answer
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Motor wdg. start and end lead identification.

03/05/2011 6:46 AM

Please do NOT use SMS in a post. We pride ourselves as professionals, slang and SMS do not fit in.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4
In reply to #2

Re: Motor wdg. start and end lead identification.

03/05/2011 7:11 AM

The most simple test for a motor is continuity. Insulation tests require a bit of experience. Go away and find what you want to do!

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Off Topic
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#9
In reply to #2

Re: Motor wdg. start and end lead identification.

03/05/2011 10:50 PM

What is SMS?

Register to Reply Off Topic (Score 5)
Guru

Join Date: Jan 2007
Location: Edinburgh, Bonnie Scotland
Posts: 1335
Good Answers: 23
#3

Re: Motor wdg. start and end lead identification.

03/05/2011 7:08 AM

Mst mtr mfgrs will have set wrng clr cde. Even if u dnt no exact mtr, cld b start pt.

__________________
Madness is all in the mind
Register to Reply Off Topic (Score 3)
Commentator

Join Date: Jan 2011
Location: Rockhampton Queensland
Posts: 67
Good Answers: 1
#10
In reply to #3

Re: Motor wdg. start and end lead identification.

03/06/2011 1:33 AM

Me, i rkn u sd bk juu. Only i sdf rank.

Wdyr

Cheers Mark N.

PS. 7+1 @ >1

__________________
I dislike "Anonymous" intensely. It is like they have something to hide? Their Cowardice.! I also dislike those Who will not help themselves, by not replying, to a civil Question.
Register to Reply Score 2 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#35
In reply to #10

Re: Motor wdg. start and end lead identification.

03/08/2011 11:45 AM

Would some kind reader please translate the above posts into something intelligible?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#5

Re: Motor wdg. start and end lead identification.

03/05/2011 8:58 AM

Some time it is possible to do this with visual inspection, but I cant tell you how to it from far.But there are other inspection method that can help you to group all starting ends and finishing ends of winding.

Check inductance L of winding 1 Between two ends

Connect winding 1 in series with winding 2 and check cumulative inductance. See if inductance is Increased (doubled) or decreased (zero)

If increased, means two ends connected for series connection are odd (finish of one winding and start of another winding) and if decreased, means two ends connected for series connection are same(either starting or finishing ends)

You can do this with all windings and make two group.

Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#33
In reply to #5

Re: Motor wdg. start and end lead identification.

03/07/2011 5:54 AM

Keep in mind this methode is not always correct. It is totally correct when you are dealing with 2 coils in a transformer, when they are on the same leg. In 3 phase motor with 6 leads, the coils are fysically displaced over 120° . The inductances will not increase to double are decrease to zero.

Register to Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#36
In reply to #33

Re: Motor wdg. start and end lead identification.

03/19/2011 9:08 AM

Thats why I have used both the words increased (double), Obviously if it don't double then it is going to increase, isn't that good enough to check the polarity,This method work fine and there is no doubt about that,Of course there can be many more ways but thats different issue,

Basic Idea is inductance in series will increase or decrease depending on what way you connect it, no matter how far they are kept and what Angle they are oriented,

Register to Reply Score 1 for Good Answer
Participant

Join Date: Sep 2016
Posts: 1
#40
In reply to #5

Re: Motor wdg. start and end lead identification.

09/13/2016 3:52 AM

I apply this method but in both conditions inductance value remain constant..

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6

Re: Motor Wdg. Start And End Lead Identification.

03/05/2011 10:48 AM

By checking the continuity with a continuit tester, you can seperate three windinsg now. Do a polarity test, with a cell & a Galvnometer.

Register to Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#7
In reply to #6

Re: Motor Wdg. Start And End Lead Identification.

03/05/2011 11:01 AM

I doubt, I think galvanometer will swing left or right depending on cell direction, not on the reversal of winding coil.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8
In reply to #7

Re: Motor Wdg. Start And End Lead Identification.

03/05/2011 8:50 PM

I am sorry! I have not explained the procedure of a polarity test. But, I have done so in the past. With careful polarity connections of the cell & the test winding as well as te Galvanometer & the check windings, it is very much possible to identify the star & end terminals of the windings.

Register to Reply
2
Commentator

Join Date: Jul 2010
Location: North West Province, South Africa
Posts: 67
Good Answers: 18
#11

Re: Motor Wdg. Start And End Lead Identification.

03/06/2011 4:24 AM

Hi cmaguna,

This reply was posted previously by me in reply to a very similar question. It would appear that this question recurs on a regular basis and perhaps a little checking of previous posts & subjects may help. I also agree with the posting regarding the use of SMS abreviations.

**************************************************************

I have been faced with this problem before with a 3 phase 380vac squirel cage motor where I received the motor back from the winders with just the six wires coming out and I had to fit the terminal block. You can solve the problem in a couple of easy steps.

1. Identify the three seperate windings with the aid of your multi-meter on the ohms range.

2. Once you have identified the windings mark the tails of each winding as follows :- winding 1 - U1 & U2 winding 2 - V1 & V2 winding 3 - W1 & W2

3. Now connect the three windings in series i.e. wire U2 to wire V1 and wire V2 to W1.

4. Connect a single phase supply (220vac) to the windings i.e. Live to wire U1 and Neutral to wire W2.

5. Switch on the single phase power to the windings and with your multi-meter measure the volt drop across the following U1 & U2, V1 & V2, W1 & W2. You will be able to see that two windings have the same volt drop and the third is different. Reverse the connections of the winding with the different reading and re-test. All three windings should now have the same volt drop.

6. Switch off the 220v power and now re-mark the coil ends from the start of the series connection you have made as U1 start & U1 finish, V1 start & V1 finish, W1 start & W1 finish.

7. Now first disconnect the three coils and then connect the windings as follows :-

U1 finish connect to V1 start

V1 finish connect to W1 start

W1 finish connect to U1 start

The windings are now connected in Delta

8. With your multi-meter on ohms check the resistance between each of the three wires marked start (U1 to V1, U1 to W1 & V1 to W1). The resistance read should be equal.

9. You are now ready to run the motor by connecting your three phase supply to U1 start, V1 start & W1 start.

10. Check the current on each of the three supply lines to the motor - they should be equal. If they aren't there is a problem and you need to recheck.

I hope this helps you out of your predicament.

__________________
A little knowledge that acts is worth infinitely more than much knowledge which is idle! Khalil Gibran
Register to Reply Good Answer (Score 2)
Member

Join Date: Oct 2010
Posts: 9
#37
In reply to #11

Re: Motor Wdg. Start And End Lead Identification.

04/09/2011 8:51 AM

hi dear,

thanks for vr. gud answer.

Regards.

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#12

Re: Motor Wdg. Start And End Lead Identification.

03/06/2011 7:50 AM

I smell smoke.

Register to Reply Score 2 for Off Topic
2
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#13

Re: Motor Wdg. Start And End Lead Identification.

03/06/2011 7:51 AM

I am assuming you have a 3ph motor here.. if not then please ignore me

you first find the winding ends using a continuity meter marking each winding end as "A" "AA", "B", "BB", "C" , "CC". use a 6 volt battery and a center zero galvanometer, connect the galvo to one pair and noting which ends are connected to the + and - of the meter, mark the winding ends as you have connected them to the meter.

Connect one of the other winding ends to one terminal of the battery and just touch the other end to the other terminal of the battery and note which way the needle of the meter moves, either to the left of the right, repeat until all the windings are done and with each test the meter needle moves in the same direction. This is called a "flick test" and if you leave the battery connected to the winding the meter will not move hence you only quickly touch the battery terminal with the winding end

you now have found the correct polarity of all three windings, so you should have three ends with a +, and three with -. Make your star point from the three + ends and connect the other three ends to your supply.

__________________
The square root of nothing is what you make it!
Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#14
In reply to #13

Re: Motor Wdg. Start And End Lead Identification.

03/06/2011 8:06 AM

You offered a good answer. But based on the light information and the spelling/grammar I don't have confidence for the poster. Maybe he can get his hands on a galvanometer or someone who knows how to use one and perform a few test runs on a set of labeled windings. Going in blind most people don't hit a home run at their 1st at bat.

I had a college professor for an electrical course who had a few sayings. His favorite one was, "electricity never forgets, you do, and when you do electricity will remind you".

Register to Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#15
In reply to #14

Re: Motor Wdg. Start And End Lead Identification.

03/06/2011 8:25 AM

low voltage batteries like 6volts can not harm human so long both terminals are not pierced in body.or user push terminals in mouth.

I think professor forget to tell you this.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#17
In reply to #14

Re: Motor Wdg. Start And End Lead Identification.

03/06/2011 9:38 AM

thank you for those few kind words.. yes I know its a good answer, as it was voted so the last time I posted it.

However your further comments regarding the OP

"But based on the light information and the spelling/grammar I don't have confidence for the poster."

It is not our place to comment on the education or the comprehension of the OP as to their understanding of English, as English MAY NOT be their first language. Therefore, we can and must TRY to understand what the OP is trying to ask, in a foreign language, in their effort to communicate.

I speak Arabic, not as fluent as I use to, and as a speaker of another language, it is EXTREMELY hard, as English is to non-speakers.

I suggest that you do not comment on the understanding or comprehension of other users of this forum.

I look at it like this.... if the OP has the intelligence to ask the question then he certainly has the inteligence to comprehend a simply explained answer.

As you speak English, all be it American English.. it is for you to decide if you can understand what the OP is asking, if not then ask another question to clear up YOUR mis-understanding of the question.. or you don't offer any answer.

Maybe your professor should have told you if you have nothing to say, say nothing.

I do not write this as an attack on you, but as a caution to your attitude as a new-bee in CR4.. The object is to help, not condemn... yes there are stupid people out there.. but do not get drawn in.

So please be nice and offer constructive and helpful comments.

Have a great day

__________________
The square root of nothing is what you make it!
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#18
In reply to #17

Re: Motor Wdg. Start And End Lead Identification.

03/06/2011 9:56 AM

My comment was on clarity, not the posters intelligence. Thanks for the condescending reprimand but I'll conduct myself according to my standards, not ones you lay down for me.

Have a nice day :)

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#19
In reply to #18

Re: Motor Wdg. Start And End Lead Identification.

03/06/2011 10:12 AM

Again.. I have to say.. if English is NOT the OP's first language then it is up to the English speakers of this forum to ensure WE have the intelligence & comprehension to understand what they want.

As for condescending.. I haven't even started if you want condescending.. and as for my standards, not mine at all, just a gentle reminder of the common standards of manners, decency and respect that should be applied here.

I agree not the clearest of questions.. however.. it was to me a lot clearer than some of the question I get asked by my trainees in Libya, Oman and other overseas countries I work in.

If you get a rise out of making fun as you've tried to do with the OP, then carry on.. however you will very quickly find your posts removed and you will find the forum will turn on you.

Again I say, I'm not having a go at you... just cool the derogatory comments.. and you will find this forum a great place to be.. and thanks.. having a great day

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#16
In reply to #13

Re: Motor Wdg. Start And End Lead Identification.

03/06/2011 9:29 AM

Are you talking of that initial back EMF glitch? That seams the only way to me with this method.

Register to Reply
Commentator

Join Date: Jul 2010
Location: North West Province, South Africa
Posts: 67
Good Answers: 18
#20
In reply to #13

Re: Motor Wdg. Start And End Lead Identification.

03/06/2011 10:29 AM

Hi Brich,

I agree with your method of using the 'Flick' test and have used this test many times to confirm the connections on CT's (both protection and metering).

One thing that I can add is that you do not need to use a centre zero galvanometer (although this would be the right meter to use) but can use a normal analogue meter set to its lowest DCV range. When you carry out the 'flick' test as you have described you would note the needle flick very slightly in one direction (either up or down).

If all three coils induce a voltage of the same polarity in the test winding (all positive or all negative deflections) then you have proved the connection of the windings. If however one reading is different then this coil is the odd one out and should be reversed.

Just as a matter of interest I have normally just used a normal 1,5 volt torch battery (D cell) to test the CT's.

Perhaps the smoke that the one poster smells is from whatever he is smoking that causes him to believe he is an expert on everything! As we would say in SA - Siestog & Shame Nogal!

__________________
A little knowledge that acts is worth infinitely more than much knowledge which is idle! Khalil Gibran
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#21
In reply to #20

Re: Motor Wdg. Start And End Lead Identification.

03/06/2011 10:51 AM

Hi Keith

I guess you could use a normal analogue meter.. never tried it myself... cannot see why it would not work. I'll remember that next time I can't find a center zero type.

Never tried the flick test on CT's.. must give that a go...

As for the smoke comment.. I'll not elaborate to any great degree as one would not wish to be dubbed condesending!!

__________________
The square root of nothing is what you make it!
Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#22

Re: Motor Wdg. Start And End Lead Identification.

03/06/2011 6:35 PM

Yes,we have the simple continuity test using a digital or analogue multimeter.

If the 6nos leads are free or connected already either in delta or star formation without any identification,remove the connections and free the 6nos leads.Set your meter at the ohm value for continuity test or use the buzzer.

Pick any one lead of the 6 leads,connect one probe(say RED) to the lead and touch the other 5 leads one after the other with the second probe(BLACK).Any lead that makes the buzzer to sound or gives continuity deflection if analogue meter is used,is the end lead of that winding,mark the leads(winding) as U1,U2.Pick another one lead of the remaining 4 leads,touch the other 3 leads,when there is sound or continuity deflection on any of the 3 leads,mark the two leads(WINDING) as V1,V2.the last 2 leads(WINDING) will be will be W1,W2.

For your motor connection in star,link W2 to U2 to V2 and take your supply L1 L2 L3 to U1 V1 W1.For delta connection,link U1 to W2,V1 to U2,W1 to V2,and take your supply L1 L2 L3 to U1 V1 W1.

__________________
Patrick Whowha
Register to Reply
Commentator

Join Date: Jul 2010
Location: North West Province, South Africa
Posts: 67
Good Answers: 18
#23
In reply to #22

Re: Motor Wdg. Start And End Lead Identification.

03/06/2011 7:59 PM

Hi Patrick,

The test you describe identifies the three windings but does not confirm that the windings are connected correctly i.e. that U1, V1 & W1 are all the 'start' ends of the winding and U2, V2 & W2 are all the 'finish' ends of the windings which is, I believe, what the OP's question concerned.

If a motor is connected to the supply (star or delta connection) with any one winding reversed then the motor, if it starts at all, will not operate correctly and will overload.

The 'flick' test described by Brich and the series test described by myself will both identify the reversed winding without opening the motor.

Hope this clears up the difference between identifying the three windings and confirming that all three windings are connected in the same direction.

Regards,

Keith

__________________
A little knowledge that acts is worth infinitely more than much knowledge which is idle! Khalil Gibran
Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#24
In reply to #23

Re: Motor Wdg. Start And End Lead Identification.

03/06/2011 9:29 PM

hello keith,

If u trace the windings and connections proper in any form of arrangement as far as u have 6 free terminal leads,and you have your U1,U2;V1,V2;W1,W2 and having made your star or delta connection,a winding in star will have 220v each for a 380v source,while in delta,a winding will have 380v each.For your L1,L2,L3 supply to U1,V1,W1,each winding of U1,U2;V1,V2;W1,W2 when traced will give you L1L2(380V),L2L3(380V),L3L1(380V) RESPECTIVELY.

__________________
Patrick Whowha
Register to Reply
Commentator

Join Date: Jul 2010
Location: North West Province, South Africa
Posts: 67
Good Answers: 18
#26
In reply to #24

Re: Motor Wdg. Start And End Lead Identification.

03/07/2011 12:29 AM

Hi Patrick,

I am definitely not trying to be argumentative but you seem to believe that once you have identified your three coils then, even if one coil is connected in the wrong direction, when you connect up in either star or delta that the motor will run OK.

My suggestion to you would be to carry out a practical test by taking a motor that is operating correctly and reverse the connection of one winding. Using your ampmeter please note the difference on each phase a) from the original correctly connected motor and the b) from the same motor with the one winding connected in reverse.

Example is for motor connected in delta but you can connect in star if you prefer.

The original motor would be connected - U2 bridged to V1, V2 bridged to W1 and W2 bridged to U1. The supply would then be applied to U1, V1 and W1.

Now reverse one winding and retest. The connection (with winding 'U' reversed) would now be - U1 bridged to V1, V2 bridged to W1 and W2 bridged to U2. The supply would then be applied to U2, V1 and W1.

I am sure after you have run this test and tried to run the motor under load you will then understand the OP's conundrum - he had six unmarked wires and has realised the importance of connecting the motor correctly - therefore the question in his posting.

Should you still be unconvinced then I would suggest you have a chat with your local motor rewind shop engineer who can explain it all to you.

Regards,

Keith

__________________
A little knowledge that acts is worth infinitely more than much knowledge which is idle! Khalil Gibran
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#28
In reply to #22

Re: Motor Wdg. Start And End Lead Identification.

03/07/2011 2:38 AM

Patrick

why make work for yourself and what you have written in your two posts is just dangerous, and not good practice.. and if you think that just by finding the ends and connecting them to the power it will work... you by admission don't have the knowledge you think you have.

You have not tried your method, if you had you would not suggest it. As suggested by Keith, you try it, but before you do, BOLT down the motor, to stop it vibrating off the bench..

The only way is to use the flick test method.. or rewind the motor.

And yes the OP has not been back and yes we are ALL assuming he/we are talking about a 3 phase motor.

__________________
The square root of nothing is what you make it!
Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#29
In reply to #28

Re: Motor Wdg. Start And End Lead Identification.

03/07/2011 3:03 AM

Good-o, as they say.

I suppose it is a productive exercise in identifying the "terminally" dangerous.

[sorry, just couldn't resist <<arha, again] the pun potential <<arha, "assuming during hysteresis" - Ahahahahaaaaaaaaaaaaaaaaaaaaaaaaaaaaa. - oh i think i wet myself...]

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply Off Topic (Score 5)
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#25

Re: Motor Wdg. Start And End Lead Identification.

03/06/2011 11:55 PM

Continuity, IR test, read for diagram, connect, IR test again. If you electrical you should know how the basic motor winding.

__________________
One system
Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#27

Re: Motor Wdg. Start And End Lead Identification.

03/07/2011 1:13 AM

Just out of interest, and I just skimmed, and it appears the OP has not been back: when/how did we decide it was a particular type of motor? or even AC?

Just curious

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Commentator

Join Date: Jul 2010
Location: North West Province, South Africa
Posts: 67
Good Answers: 18
#30
In reply to #27

Re: Motor Wdg. Start And End Lead Identification.

03/07/2011 4:20 AM

Hi 34point5,

No, it doesn't appear as if the OP has returned to the discussion however that is irrelevant for me as his question has started an interesting discussion which is why I subscribe to CR4 in the first place. Just for your information the OP may have read all the replies in the discussion and just not posted his response.

I should point out that his description of a motor with six leads led us to believe that it was indeed a 3 phase AC motor and if you have a look at my postings you will note that I categorically stated that I was referring to a 3 phase AC motor with the exception of the post where I referred to the 'flick' test as used (in my experience) to check CT's.

As in all forums there will be those who choose to post nonsense and ridicule posters who struggle with their use of English. One should remember that a posters inability to communicate clearly in English in no way indicates that they are technically or mentally incompetant. The fact that you are reading this on a Chinese or Korean manufactured monitor that has been designed and manufactured by people who have no knowledge of even one English word should bear witness to this.

When reading through CR4 one should bear in mind that there are 'diamonds amongst the stones' and it is these diamonds that make it such an interesting and informative site.

You actually make a point of saying that the OP has not returned - this could probably be explained and caused by the poor responses to his posting. I actually live in a country where we have eleven official languages and am very aware of the arrogant belief held by many English speakers that you are uneducated if you are not fluent in English. I can imagine an English speaker arriving on Mars and asking a Martian "Do you speak English?"

I qualified over 42 years ago and one of my ambitions is to share my technical experience with the newly qualified Engineers and Technicians. Even today I believe that if I don't learn something during the course of the day it will have been a day wasted. All I am expecting is for the rest of the posters who believe that their brand of wit (asking what colour the motor is or smelling smoke over the net) should try to restrict their comments to comments that reflect their 'superior knowledge' and maintain their dignity.

Regards,

Keith

__________________
A little knowledge that acts is worth infinitely more than much knowledge which is idle! Khalil Gibran
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#31
In reply to #30

Re: Motor Wdg. Start And End Lead Identification.

03/07/2011 4:30 AM

had to give a GA!

I did not realize that in SA you were so articulate... joking.. I promise.. :)

__________________
The square root of nothing is what you make it!
Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#32
In reply to #30

Re: Motor Wdg. Start And End Lead Identification.

03/07/2011 4:48 AM

Good-o Keith

Do you have some ESL issue with post #1?

Or, with my having a bit of a hoot with Brich, who is obviously 'concerned' by 'creative solving' outcomes - all based on 'assume'.

You have no way of knowing if in fact these wires are 'actually encoded' - by say stripes - the OP can't grasp the significance of. Or vary in diameter - a whole other set of variables.

But for what it's worth my history on CR4 should tell you: You have no way of 'mounting an ESL smear campaign' on me especially.

If you wish, you may post in Afrikaans and I will be one of those that understand.

So what is your actual 'point'?

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Guru

Join Date: Jun 2007
Posts: 1035
Good Answers: 40
#34

Re: Motor Wdg. Start And End Lead Identification.

03/07/2011 9:30 AM

As cmaguna (OP) hasn't found his way back, YET ... I'll throw-in. (Perhaps he has just figured out how to SEARCH for an identical post, before posting his own...?)

For ease of typing, I repeat my Post (#6) at THIS THREAD ... [quite similar to the GA by 34point5 (Post#1)] ... Note: this is a "link-within-a-link" response...

Register to Reply
Participant

Join Date: Oct 2012
Posts: 1
#38

Re: Motor Wdg. Start And End Lead Identification.

10/13/2012 7:08 AM

A simple method for identifying the start and end connections are:

Take windings U1-U2 & V1-V2. connect them in series (short U2 and V1 ) with a lamp(230V) and apply a 1 phase voltage across that. If the voltage across the lamp reads less than 230V(approx. 220V) then the start and end connections are correct. If the voltage across the lamp reads same as that of applied voltage then we have reverse the start and end connections. Reapeat the same for V1-V2 & W1-W2.

Register to Reply
Commentator

Join Date: May 2010
Location: UK
Posts: 89
Good Answers: 2
#39
In reply to #38

Re: Motor Wdg. Start And End Lead Identification.

10/13/2012 9:18 AM

would you like to post a diagram for your suggestion?

Register to Reply
Register to Reply 40 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

34point5 (4); brich (6); cmaguna (1); cwarner7_11 (1); electricalexpert65 (2); Fredski (3); GM1964 (1); Keith Grewar (5); loadshare (1); Maanu (1); Markone (1); ndt-tom (1); Patrick Whowha (2); PWSlack (1); rajaswi (1); rakesh_semwal (5); rudy.leurs (1); thccontrols (1); TonyS (2)

Previous in Forum: Design Control And Power Circuits   Next in Forum: Voltage Optimisation

Advertisement