Difference Between Insulation Rated Voltage and Rated Impulse Voltage?

03/07/2011 12:19 AM

what is the difference between insulation rated voltage and rated impulse voltage

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: mcb

03/07/2011 8:33 AM

Rated Insulation Withstand Voltage (Ui) is the voltage at Power Frequency (50 Hz or 60Hz) that might appear across the phases of the MCB, due to voltage fluctuations in the system (Supply Fluctuations and Transformer Tap Actions). This might prevail for a longer duration till corrective actin is taken. MCB has to withstand this POWER FREQUENCY OVER VOLTAGE. The capacity of the MCB to withstnad this voltage is called its Rated Inulation Withstand Voltage (Ui). Typically it is 690V for a 415V System

On the other hand, Rated Impulse Withstand Voltage (Uimp) is a non-power-frequency over voltage of very high magnitude, but appearing for a very short duration (typically, in micro seconds); they are also called surges or transients. the main cause for such transients are Lightning Surges & Switching Surges. The magnitude can be of the order of 8kA (in a 415V System). The MCBalso has to withstand this transient overvoltage. The capacity of the MCB to withstand this TRANSIENT OVER VOLATGE is called its Rated Impulse Withstand Volatge (Uimp). It is generally 8kV for a 415V System.

Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Mar 2011
Posts: 16
#2

Re: Difference Between Insulation Rated Voltage and Rated Impulse Voltage?

03/07/2011 9:25 PM

I think. insulation rated voltage is voltage that system will work at rated frequency and the manufacturer require the equipment must be operated under rated voltage if not, the insulator of equipment will damage.

rated impulse voltage is voltage that equipment can only bear in a short time then the relay in system will interrupt and equipemt will be still safe

Register to Reply