what is the difference between insulation rated voltage and rated impulse voltage
Good Answers: 170
Re: mcb
03/07/2011 8:33 AM
Rated Insulation Withstand Voltage (Ui) is the voltage at Power Frequency (50 Hz or 60Hz) that might appear across the phases of the MCB, due to voltage fluctuations in the system (Supply Fluctuations and Transformer Tap Actions). This might prevail for a longer duration till corrective actin is taken. MCB has to withstand this POWER FREQUENCY OVER VOLTAGE. The capacity of the MCB to withstnad this voltage is called its Rated Inulation Withstand Voltage (Ui). Typically it is 690V for a 415V System
On the other hand, Rated Impulse Withstand Voltage (Uimp) is a non-power-frequency over voltage of very high magnitude, but appearing for a very short duration (typically, in micro seconds); they are also called surges or transients. the main cause for such transients are Lightning Surges & Switching Surges. The magnitude can be of the order of 8kA (in a 415V System). The MCBalso has to withstand this transient overvoltage. The capacity of the MCB to withstand this TRANSIENT OVER VOLATGE is called its Rated Impulse Withstand Volatge (Uimp). It is generally 8kV for a 415V System.
Re: Difference Between Insulation Rated Voltage and Rated Impulse Voltage?
03/07/2011 9:25 PM
I think. insulation rated voltage is voltage that system will work at rated frequency and the manufacturer require the equipment must be operated under rated voltage if not, the insulator of equipment will damage.
rated impulse voltage is voltage that equipment can only bear in a short time then the relay in system will interrupt and equipemt will be still safe