Gen Current Sharing

03/06/2011 8:17 PM

I need help re generator kvar sharing. what is the main reason why is the gen in parallel got a big difference in current, our gen is 230 kw, 440 volts 60 hz ang we are using mechanical governor. any adjustment to make the current of both gen at least to be closed in value each other. thanks in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Gen Current Sharing

03/06/2011 8:52 PM

Why don't you share a little lot more information. Do you mean KVA or KVAR? What is the shared load amps and how is it divided? Both generators = 230 kw? What have you done to balance the load?

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#2

Re: Gen Current Sharing

03/06/2011 11:32 PM

Important point when you will paralleling the sets are same phase rotation, freq and voltage. In freq and voltage not only same value but also droop. This will effect when you already parallel and load, changing in load will cause different loadsharing between gensets if the droop doesn't meet the same level.

Hope this help you

__________________
One system
Register to Reply
Associate

Join Date: Aug 2010
Location: bhubaneswar
Posts: 34
Good Answers: 1
#3

Re: Gen Current Sharing

03/07/2011 12:17 AM

You should have the same rpm,freq.,voltage.these are the importance things for paralleling the generator.But you should use equalizer between the generator to ensure the proper load sharing between both generators.Then you will have nearly equal current.

Register to Reply
2
Commentator

Join Date: Feb 2011
Location: Dubai, UAE
Posts: 63
Good Answers: 7
#4

Re: Gen Current Sharing

03/07/2011 7:11 AM

The response of the governor to load variation is not always exactly matching (in both machines) which is causing the problem, not a big issue follow the O&M manuals and adjust the screw / lever settings of the mechanical governor for a nearly symmetrical response.

Register to Reply Good Answer (Score 2)
Power-User
Engineering Fields - Petroleum Engineering - Rig Electrician United States - Member - the Oil Patch Engineering Fields - Power Engineering - Drives & Gen's Engineering Fields - Instrumentation Engineering - Drive Control Popular Science - Cosmology -

Join Date: Jan 2010
Location: Houston off/on-shore @ Oil Patch
Posts: 223
Good Answers: 2
#5
In reply to #4

Re: Gen Current Sharing

03/07/2011 1:37 PM

Check if you can adjust the Voltage Regulator and balance amps with that adjustment on each Gen on line AFTER you get the best you can (look at KW's) with the Speed Regulator like Khi says.

__________________
Why do they make manhole covers round? so they won't fall in [before asking "Who is John Galt?"]
Register to Reply Score 1 for Good Answer
Anonymous Poster #1
#6

Re: Gen Current Sharing

03/07/2011 11:15 PM

In generator synchronizing we must look on three quantities ie. KW, KVA & KVAR shearing by each generator. If ur KW shearing is ok that means governor is ok, then for KVAR shearing check excitation voltage regulator (AVR) of both generators because for KVAR shearing we increase OR decrease excitation voltage.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#7

Re: Gen Current Sharing

03/08/2011 7:15 AM

If both generators are rated the same 230kW etc, and /or are of the same make, then:

1- Check the AVR settings: there is a DROOP setting usually, (a Potentiometer marked Voltage droop) which will be set the same on both generators. Also, a gain potentiometer, which is used to adjust the voltage gain when the load varies: Also, they must be the same. How:?

a) Run each genset separately and load it to ~75% if possible, and adjust the Voltage gain potentiometer to have the desired voltage without flickering (i.e. the voltage is stable, use an incandescdent lamp to see that it is not changing intensity periodically, or an analog voltmeter and look at the needle vibrations). if too much gain, the voltage will be varying (hunting) with more or less frequency: turn the pot to reduce the period until zero, and a little more. Also, adjust the main voltage pot to have the 440V at no load or low loading.

b) The droop setting: there are usually graduations to help setting. use then to set at the same graduation. Then check how much the voltage on each genset, will drop from no load to full load: It must be the same, otherwise adjust the droop for one of them to match the other.

2- The mechanical governor: They also have a droop setting screw if they are built for parallelling. This will adjust the rpm drop from no load to full load. They should be at the same setting for both engines if they are of the same capacity (similar engines and alternators). To set, run the engines from no load to near full load (~75%)separately and check that they keep the same rpm at each position from no to full. otherwise, adjust the One to match the other. Choice depends on the state of the engines (age and other variables) so that they will droop the same way and the minimum possible from the set Frequency.

If the above is done properly, both engines will share the load kW and kVAR. if the error in loading is +/- <10%, you are OK (you will look at the current Amps differential for that: ex: in your case ~30 to 35A difference).

I hop the above will help. this is not the 1st time in this forum. you can search for parallelling two generators...

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Dec 2010
Posts: 11
#8

Re: Gen Current Sharing

03/09/2011 5:40 AM

Thank you so much for all your valuable info. appreciated very much. We tried to perform all hints, but the fault still persisted. the kw & hz are same both genies during running operation, but I wonder why the difference of current is too high, about 50 amps diff. anyway, we will try more solution.thanks again to all who respond.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#9
In reply to #8

Re: Gen Current Sharing

03/09/2011 5:48 AM

One more thing: The Neutral of One machine is to be used preferably. The 2nd machine neutral can be isolated from the load busbar neutral. this might help reducing the excess current circulating ...

If you need to run each genset on its own from time to time, then a neutral switch/contactor should be provided for when the genset is running single.

Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#10
In reply to #8

Re: Gen Current Sharing

03/09/2011 5:54 AM

You do realize that is ± 4.7%

And kW & Hz are the same ....

So what are the tolerances on your ammeters, CT's and/or shunts?

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#11

Re: Gen Current Sharing

02/21/2013 4:01 AM

Dear Mr. delta72924,

The Load sharing of Generator, mainly depends upon the VOLTAGE DROOP CHARACTER.

You consider two Generators, of 420 Volts, and same capacity. If 1st Generator Voltage Drop (known as DROOP CHARACTER) from No-Load to Full Load is ( for example) is 20 Volts, and for the 2nd Generator, Voltage Drop is 25 Volts, 1st Generator will share 25/45 = 0.55 or 55% and the 2nd Generator will share 20/25 = 0.444 = 44.4%, or rounded to 45%, to balance Mathematics, as 55+45=100.

The Generator with LESS VOLTAGE DROP, will SHARE MORE LOAD than the other Generator which has High Voltage Drop since the UNDER SYNCHRONISED CONDITION THE VOTAGE DROP at the GENERATOR Terminal SHOULD BE COMMON, for both Alternators which is achieved, by extra load sharing, by the Generator which has Less Voltage Drop from No-Load to Full Load.

This is a simple explanation/answer.

DHAYANANDHAN.S

Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

34point5 (1); A.A.Khi (1); Anonymous Poster (1); delta72924 (1); dhayanandhan (1); kwcharlie (1); LAA_Lucke (2); loadshare (1); manvendra (1); wareagle (1)

Previous in Forum: Power Calculation   Next in Forum: Difference Between Insulation Rated Voltage and Rated Impulse Voltage?

Advertisement