Anonymous Poster #1

Faulty 3 Phase Load

03/07/2011 3:42 AM

We have an old oil filter machine with star connected(floating neutral) resistive load as heater. What happens if any phase load go faulty(open circuit)? I said the imbalance in 3 phase leads to rise in voltage in other phases. How much does it affect the other phase loads/coil so that my electrician gets satisfied with my answer.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: 3 phase load

03/07/2011 3:59 AM

If one heater element short-circuits, the voltage in the other two will multiply by √3, the current by √3, and the wattage by 3. Possible burnout.

If one element fails open, the voltage in the other two will reduce by (√3)/2, the current by (√3)/2, and the wattage will be 3/4 of before. They won't get as hot.

I don't think a corner ground-fault will make any difference to the heater elements.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster #1
#2
In reply to #1

Re: 3 phase load

03/07/2011 4:51 AM

Thats reasonable i believe you but i can't stand by the concept unless i find a proof for it myself. Thank you sir.

Reply
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: 3 phase load

03/07/2011 5:22 AM

In one sense, this is just a matter of simple geometry. A 3-phase system is a triangle with the vertices receiving line power. If there is a neutral, it may be at the center of the triangle (most common), at the center of one side of the triangle, or at one corner of the triangle (least common, but some systems are like that).

The voltages are proportional to the lengths of the lines involved, and the phase angles are the same as the angles between whichever lines. If there is an earth fault, the neutral point moves accordingly, which distorts the triangle, but the voltages and phase angles still match the shape and size of the distorted triangle.

In your system, if the 3 heaters are identical, they establish a neutral at the center of the main triangle. An open heater moves the neutral to the midpoint of one side. A shorted heater moves the neutral to the vertex where the short is. In either case, the voltage can be determined by simple inspection of the diagram.

It is sometimes called a "phasor" or "vector" diagram. Not all field electricians know this, but some do; electrical engineers usually do, but there seem to be some exceptions....

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Good Answer (Score 2)
Anonymous Poster #1
#4
In reply to #3

Re: 3 phase load

03/07/2011 5:48 AM

Well as far as you are preoccupied in your mind ''not to explain that topic''.I told i should study it myself. I missed the class and no way its easy to learn from books. Thanks for the inspiration.

Reply Off Topic (Score 7)
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#5

Re: Faulty 3 Phase Load

03/07/2011 11:52 PM

The heater system is star connected, if one element goes open circuit the only problem you would have is that you would have an unballanced load as one phase would not be operational, it would also take longer to reach the target setpoint temperature, that is if it is able to reach the target temperature.

You have to understand that when the elements are star connected, and you have a resistive load connected ohm's law comes into play. Between phases you always have 2 elements connected in serries, if an element burns out and is open circuit you only have now 2 elements connected across 2 of the phases and this is exactly what you would have even when all the elements are operating.

Lets say the elements are 50 ohms each, when wired in serries that is 100 ohms across 2 phases, so V/R=I 400/100 = 4 amps this is the line current, this would not change as the load is resistive, all that would happen is you would is you would loose the heating ability of one of the elements, nothing else, there is no danger of having a cascading effect of burning out the other elements.

If you or your electrician are so concerned about this, you could always instal a 3 phase thermal overload to monitor any irregular phase imballance and raise an alarm or shut down the heater, which ever is perferred.

Also you mentioned about a voltage rise, the only voltage rise that could happen is to the phase that is not operating when the element is open circuit, but this voltage could not rise any higher than the supply voltage, as the circuit is not inductive.

I hope this answers your question,

Cheers

Joe

Reply Score 1 for Good Answer
Anonymous Poster #1
#6
In reply to #5

Re: Faulty 3 Phase Load

03/08/2011 2:42 AM

I dont think the thermal overload relay works here.In the case of open circuit fault in one phase of 3 phase load the voltage and current is reduced to sqrt3/2 and power to 3 in other 2 phases. It will work for short circuit fault. I was looking for the vector representation of faults in any phase. The answer is well explained with the help of triangle but i am so dump that i need more attention on topic. Thank you guys

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7
In reply to #6

Re: Faulty 3 Phase Load

03/08/2011 3:16 AM

You might not have practiced this much yet (or be out of practice), but you're asking the right questions and grasping the ideas.

I need to add a technicality to the earlier post 3. The triangle is an oriented triangle; think if it as having arrows going clockwise around. Although the corners are 60° angles, as vectors each side is rotated 120° from the next.

A higher level of generality about this is transformer vector groups. Wikipedia has a good article on this.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#8
In reply to #6

Re: Faulty 3 Phase Load

03/08/2011 4:14 AM

I would have to agree with you. You dont have much understanding of electrical control do you?

Let me explain: If you have a 3 phase overload in the circuit it monitors the circuit just as if an inductive motor was connected, if you loose an element it is the same as loosing a phase, the overload will trip because of the imballance of the phase currents.

Forget about all the other crap (no offence to other threads). Your question was about if an element went open circuit, my answer still stands.

Do you know what happens if you loose 2 Elements? You will have no heat, if they are wired in a floating star formation.

If you need to monitor the circuit, for an open circuit, use a 3 phase overload.

Trust me on this one.

Cheers

Joe

Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9
In reply to #8

Re: Faulty 3 Phase Load

03/08/2011 4:32 AM

Overload devices don't detect phase imbalances or losses unless the remaining phase currents increase. This may happen with inductive loads like motors, but an open heater element in this scenario results in a modest drop of currents in the remaining elements, which goes right under the radar screen or normal overload devices. A phase protection relay (different animal) could work, though.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#10
In reply to #9

Re: Faulty 3 Phase Load

03/08/2011 5:08 AM

Tornado

Well I thought 3 phase overloads were about monitoring the current on each phase, I may be wrong, But tell me why when we are using a single phase load through a 3 phase overload we tend to wire the overload in series, modern overloads don't just monitor overcurrent, they also monitor the current in each phase, older thermal overloads also do the same thing. Try connecting a single phase load to a 3 phase overload, Without wiring the overload in serries.

Thermal Overloads on a 3 phase system heat at the same temperature, If we loose a phase on a motor, one of the overloads cools or possibly another overheats and this causes the tripping, Correct me if i am wrong.

Best Regards

Joe

The Truth Shall Set You Free

Reply Score 1 for Good Answer
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#11
In reply to #10

Re: Faulty 3 Phase Load

03/08/2011 7:33 AM

Joe, You are correct on all the points! GA

The OP must understand something about the flow of electric current and the laws (Ohms law at least...).

One element ==> open circuit ==> heat reduced by 1/3 from original setting with 3 on a 3 phase START. No changes in voltages on each phase. And yes, the normal 3 phase Overload used for inductive motors, with thermal bimetals ... will trip due to unbalanced heating of the elements.

Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#13
In reply to #11

Re: Faulty 3 Phase Load

03/08/2011 1:59 PM

Thanks for the GA

Reply
Power-User
Canada - Member - New Member

Join Date: Feb 2010
Location: The Great White North
Posts: 185
Good Answers: 13
#12
In reply to #10

Re: Faulty 3 Phase Load

03/08/2011 12:50 PM

I Think I'll have to agree with Tornado.

On the old solder pot overloads a lost phase on a resistive load will not trip the overload since the 2 remaining phases do not exceed thier original current.

On newer style overloads they would likely trip on imballance, and not overload. For the same reason.

__________________
Knowledge makes what was impossible, seem easy.
Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#14
In reply to #12

Re: Faulty 3 Phase Load

03/08/2011 2:07 PM

Elroy, you are correct about the solder pot overloads, these would not be suitable for this application, for the reason you stated.

When I mentioned older thermal overloads, I was refering to the Bimetal type of overload.

I have not seen a solder pot overload, for at least 20 years, in fact the last one I worked on was in 1988 in a factory in Dunedin, and I bet that factory is still using them.

Cheers

Joe

Reply
2
Power-User
Canada - Member - New Member

Join Date: Feb 2010
Location: The Great White North
Posts: 185
Good Answers: 13
#15
In reply to #10

Re: Faulty 3 Phase Load

03/09/2011 8:57 AM

Bimetallic overloads for single phase.

There are two reasons why the bimetallic overloads need to be wired in series.

1) The power required for tripping the switch mechanism can only be generated by three bimetallic strips together. The three bimetallic relays have to be wired in series, to ensure that a current flows through all of them during single-phase operation.

2) Tripping on differential overload would occur if this is not done.

If the center phase was to open, the center phase bimetallic element is not deflected because no current flows. The other two phases are deflected because of flowing current. The difference between the deflected and un-deflected elements causes the overload to trip. In this way a lost phase would cause a trip of the overload. This is the action that I believe you are referring to.

We still use hundreds of starters with solder pot or as Allen Bradley calls them eutectic overloads. These overloads do not have differential tripping and would not be suitable for 3 phase resistive applications.

Have a good one Elroy

__________________
Knowledge makes what was impossible, seem easy.
Reply Good Answer (Score 2)
Anonymous Poster #1
#16
In reply to #15

Re: Faulty 3 Phase Load

03/09/2011 11:43 AM

Elroy

thanks for introducing differential protection in 3-phase i don't know the concept is used for bimetallic strip for phase imbalance(apart from OL protection ).

Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#17
In reply to #15

Re: Faulty 3 Phase Load

03/09/2011 1:40 PM

Hi Elroy,

That was exactly what I meant to say, so you get a GA from me.

Your wording and detailed explanition was very good

Cheers

Joe

Reply
Anonymous Poster #1
#18
In reply to #17

Re: Faulty 3 Phase Load

03/10/2011 10:34 AM

well guys

I'm interested to share some pics of the "oil filtering plant".It remind me of an old Russian military device in video games.

& the connection

....

Reply
Power-User
Canada - Member - New Member

Join Date: Feb 2010
Location: The Great White North
Posts: 185
Good Answers: 13
#19
In reply to #18

Re: Faulty 3 Phase Load

03/10/2011 11:50 AM

It looks like you've got your work cut out for you. Safety must not have been a big concern where this machine came from. I'm guessing the wires in the bottom picture are connected to the heating elements but I don't see any filters.

__________________
Knowledge makes what was impossible, seem easy.
Reply
Anonymous Poster #1
#20
In reply to #19

Re: Faulty 3 Phase Load

03/10/2011 7:29 PM

Yes you are right.The star connected heaters draws 30Amps and i could see its connected directly with 30Amps capacity contact.There is only one OL relay for vacuum pump. The filter is in the front side enclosed. A lot of valves,termostat,pressure guage etc. its oil flow is alien for me.

Reply
Reply to Forum Thread 20 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (6); Elroy (3); Joe Sparky (6); LAA_Lucke (1); Tornado (4)