Can someone give me information on Power Frequency Testing for EHV 220kV or 400kV Cables and the equipments used in testing with budgetary cost and make of the test equipments ?

Register to Reply
Pathfinder Tags: cable testing ehv power frequency
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#1

Re: Power Frequency Testing for EHV Cables

04/05/2007 11:17 AM

I would recommend contacting Hipotronics (http://www.hipotronics.com).

They are part of Hubbell, Inc. and make a full line of the kind of testing equipment you are looking for. Haefely, Tettex and Robinson Instruments are also part of Hipotronics.

Hipotronics

1650 Route 22

P.O. Box 414

Brewster, NY 10509 USA

Phone: 1-800-727-4476

Fax: 845-279-2467

I think they will be able to answer all your questions.

Register to Reply
Guru
Popular Science - Weaponology - New Member

Join Date: Feb 2006
Posts: 962
#2

Re: Power Frequency Testing for EHV Cables

04/06/2007 3:04 PM

What do you mean power frequency testing it makes no sense. Do you mean load test and or max voltage test? (Break down teasting?) more info would help.

What do you class as EHV any way? If you do not know keep well away from any such equipment it can be fatal to try, if you make a mistake all they will find is a pile of ash.

__________________
There's them that knows and them that just thinks they know, whitch are you? Stir the pot and see what rises up. I have catalytic properties I get a reaction going.
Register to Reply
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#3
In reply to #2

Re: Power Frequency Testing for EHV Cables

04/07/2007 11:29 AM

Actually, power frequency testing of cables makes perfect sense (although for EHV cables, acceptance or proof testing after installation is normally done with DC due to the high cable capacitance and associated charging current).

Power frequency tests by a cable manufacturer could include withstand, puncture, partial discharge, thermal, capacitance, power (dissipation) factor, life, etc.

Extra High Voltage (EHV) is a class of transmission system voltage which, in the USA, is 345 - 700 kV nominal (362 - 765 kV maximum). System voltages above EHV are classified as Ultra High Voltage (UHV).

Standard transmission voltages in the USA are covered by the American National Standards Institute (ANSI) Standard C-84.

Register to Reply
Participant

Join Date: Apr 2007
Posts: 3
#4
In reply to #3

Re: Power Frequency Testing for EHV Cables

04/09/2007 12:06 AM

Dear Sir,

Thanks for your information. Here in India the standard voltage ranges from 11kV, 33kV,66kV,110kV, 220kV,400kV and 765kV. 765kV is very rare in India.

We want to start are new line of business of providing the service of CABLE TESTING during commissioning and are looking out to purchase the required testing equipments.

We are willing to invest on the required infrastructure as the future of Power Sector in India is good both in the short term and long term. There are very few in the country who provide this kind of service.

Can you please recommend some of the field testing equipments that are used in testing of 220kV and 400kV cables during commissioning.

I am sure your information will aid in better decision making at our end.

Best Regards

R.T. Selvam

Chennai

India.

Register to Reply
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#5
In reply to #4

Re: Power Frequency Testing for EHV Cables

04/10/2007 8:52 PM

I'm familiar with the grid in India. Spent some time with the TATA Group and National Grid about 12 years or so ago. I also have experience testing underground high pressure pipe type, low pressure oil-filled and solid dielectric underground cable.

The field test equipment you need is generally self-contained as part of the test set. Every field test set I have ever used was manufactured by Hipotronics. Many were owned by the electric utility because they were also used by their maintenance groups. Most of them were mobile and mounted on trailers.

You might review Grid's specifications for UG cable systems and see what kinds of tests they presently require. You probably want to consider offering diagnostic testing and maintenance services in addition to commissioning.

Then, I would refer you to response #1 and recommend that you contact Hipotronics. I'm sure they will be willing to discuss the kinds of test equipment in use by others and recommend a solution for you.

Good luck.

Register to Reply
Anonymous Poster
#6
In reply to #4

Re: Power Frequency Testing for EHV Cables

05/01/2008 8:01 AM

Hello,

Have you purchased the equipment for cable testing?.

I have used different types of equipments in the field as i was in the power utility company.It depends upon at what voltage level you want to play with.But all the equipments have to be imported for which players are available in india.